Still a relatively inexperienced so sorry if these seem obvious/dumb questions.
I wanted to spur a double socket next to an existing double socket in a bedroom in my own house on the first floor, sounded like a good idea!
EDIT: Isolated the circuit 1st!!
My first worry.
I loosen the socket face place and get my continuity tester. I place my continuity tester across live+neutral terminal screws and I get a voltage warning (no scale just a warning)? Plugged in my Metrel and it's reading 1V. Not really happy about this so I isolate the supply and everything seems OK back to 0V.
1st Question. Is this normal? I have isolated single circuits before and can't remember this happening. Continuity tester is proved to be working OK etc.
Anyway, all safe so I take off the socket face plate. The book Part P Dr (second Fix) suggests to check you have a ring before you begin. So I measure r1, rn and r2 at the socket.
r1 comes in at 0.36Ω
rn comes in at 0.36Ω
r2 comes in at 0.19Ω??? I was expecting 0.6Ω. The cpc is obviously not thicker than the live conductors nor is it the same size. It looks like 2.5/1.5mm T+E to me!
Re-took r1, rn and r2 and I got the same.
Put everything back and go to the consumer unit.
Find the ring circuit (cringe at finding the neutrals practically fall out of the terminal block!) and disconnect the ring to take r1, rn and r2.
r1 comes in at 0.35Ω
rn comes in at 0.36Ω
Hmm r2 comes in at 0.43Ω. Still lower than I what is expected.
Zs from the socket is 0.30Ω for a Type 2 32A MCB which is perfectly fine according to the OSG.
I noticed there is another socket a bit loose on the same ring and take that off to have another look. Find this has a spur already. No diagrams available etc (as normal).
With such a low r2 reading all I can assume is somewhere there is a parallel path? There is lot of suplementary bonding in my house. It was built around 20 years ago now. Anyone got any thoughts or things I should try to work out wth is going on?
Many thanks.
I wanted to spur a double socket next to an existing double socket in a bedroom in my own house on the first floor, sounded like a good idea!
EDIT: Isolated the circuit 1st!!
My first worry.
I loosen the socket face place and get my continuity tester. I place my continuity tester across live+neutral terminal screws and I get a voltage warning (no scale just a warning)? Plugged in my Metrel and it's reading 1V. Not really happy about this so I isolate the supply and everything seems OK back to 0V.
1st Question. Is this normal? I have isolated single circuits before and can't remember this happening. Continuity tester is proved to be working OK etc.
Anyway, all safe so I take off the socket face plate. The book Part P Dr (second Fix) suggests to check you have a ring before you begin. So I measure r1, rn and r2 at the socket.
r1 comes in at 0.36Ω
rn comes in at 0.36Ω
r2 comes in at 0.19Ω??? I was expecting 0.6Ω. The cpc is obviously not thicker than the live conductors nor is it the same size. It looks like 2.5/1.5mm T+E to me!
Re-took r1, rn and r2 and I got the same.
Put everything back and go to the consumer unit.
Find the ring circuit (cringe at finding the neutrals practically fall out of the terminal block!) and disconnect the ring to take r1, rn and r2.
r1 comes in at 0.35Ω
rn comes in at 0.36Ω
Hmm r2 comes in at 0.43Ω. Still lower than I what is expected.
Zs from the socket is 0.30Ω for a Type 2 32A MCB which is perfectly fine according to the OSG.
I noticed there is another socket a bit loose on the same ring and take that off to have another look. Find this has a spur already. No diagrams available etc (as normal).
With such a low r2 reading all I can assume is somewhere there is a parallel path? There is lot of suplementary bonding in my house. It was built around 20 years ago now. Anyone got any thoughts or things I should try to work out wth is going on?
Many thanks.