Hi

I have installed a ring with 7 sockets on it

when insulation resistance testing these are the results i get

L-N >500Mohms
L-E >500Mohms
N-E 6.8Mohms

as this is a new circuit i am not willing to accept the N-E reading of 6.8Mohms as i consider it well low although it does pass the regs.


Thing is if i split the ring at the first socket and test both ends of the cable at the CU i get >500Mohms and if i test at both ends of the disconnected socket same reading >500M ohms. I thought this may mean a faulty socket so i put the cables into a connector block at the socket and i get the same low reading when i test at the board.

Has anyone got any suggestions?

Thanks

Matt
 
Have you proved the continuity of the ring yet?

If not you might be breaking the ring in a second place and disconnecting the fault.
 
Have you proved the continuity of the ring yet?

If not you might be breaking the ring in a second place and disconnecting the fault.

continuity has been checked and results were as follows

L-L loop 0.35 ohms
N-N loop 0.35 ohms
E-E loop 0.6 ohms

ill recheck these results tomorrow though
 
One of the back boxes with moist plaster over the neutral/earth connection terminals? If the IR has improved tomorrow (plaster dried out) it could well be that...?
 
Keep your tester going and take off and wiggle each socket, when the reading changes you know where to look for a problem, that's still a fairly high reading so it's probably not going to be anything obvious to the eye.
 
sorted thanks guys. broke the ring back down into smaller sections and found one of the capping nails had penetrated the cabe. luckily i was doing a quick test before getting a spread on the go
 

Reply to Ring Circuit testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
814

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332
Well we called it a room, but it was only a hole in the ground covered with bit of canvas.
Replies
13
Views
639

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top