Bennewman

I'm rather new to testing and interpreting results. Did a test two weeks ago on a new ring installed then with continuity results L-L 0.37, N-N 0.36, E-E 0.60 and L- E 0.25. All good. Tested it today and got results L-L 0.17, N-N 0.17, E-E 0.39, L-E 0.05. Not good. I'm testing it again tomorrow and I think I know where I went wrong. I didn't null the leads, either two weeks ago or today. (notice today's results are all approx. .2 ohm less than two weeks ago). My confusion is that I'm assuming the results I got two weeks ago are correct and today's are wrong...but, how could I have taken OFF .2 ohms by not nulling the leads today??? Or two put it better, how can nulling the leads add .2 ohm??
 
you probably didn't null the leads the first time. that would account for the higher reading. i can't see where the L-E reading comes in when you're testing e-e on a ring.
 
Yes but the original figs calculate correctly. the new one's don't. I can't have an E- E reading more than double the L-L. should be approx. 1.67 right? Also, I can't have an L-E at sockets after cross connecting at 0.05 if the E-E is 0.39 and the L-L is 0.17. That's why I'm assuming the original figs are right and the new one's are wrong. But how can I add resistance by not nulling. It's not possible, right?
 

Reply to Ring continuity test results. Help please. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
917
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
277
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top