A

amckay

If a ring final circuit is to be extended what would be the appropriate cert to issue? I was thinking it to be a MWC but I'm not sure if it should be an EIC.
I think it should be a MWC as its not a new circuit, just slightly bigger/longer but I'm not sure and my regs book is on site so can't refer to it.
Thanks
 
If a ring final circuit is to be extended what would be the appropriate cert to issue? I was thinking it to be a MWC but I'm not sure if it should be an EIC.
I think it should be a MWC as its not a new circuit, just slightly bigger/longer but I'm not sure and my regs book is on site so can't refer to it.
Thanks

This is how it is worded in BS7671.


The minor works certificate is intended to be used for additions and alterations to an installation that do not extend to the provision of a new circuit. Examples include the addition of socket-outlets or lighting points to an existing circuit, the relocation of a light switch etc. This certificate may also be used for the replacement of equipment such as accessories or luminaires, but not for the replacement of distribution boards or similar items. Appropriate inspection and testing , however, should always be carried out irrespective of the extent of the work undertaken.
 
If a ring final circuit is to be extended what would be the appropriate cert to issue? I was thinking it to be a MWC but I'm not sure if it should be an EIC.
I think it should be a MWC as its not a new circuit, just slightly bigger/longer but I'm not sure and my regs book is on site so can't refer to it.
Thanks
it depends on how many points and how much actual installation is involved, a MWC is acceptable provided the new continuity of ring, R1 + R2, and Zs are recorded. If you're extending the rmso
by 20 points installing new conduit , trunking, and 30 metres of cable, then MWC is probably not the way to go
:)
 
If you're extending the rmso
by 20 points installing new conduit , trunking, and 30 metres of cable, then MWC is probably not the way to go
:)
Considering that Simon has quoted direct from the regs what are you basing that statement on?
At what point are you going to change from a Minor works to an EIC?
Not having a go at you, just wondering what your thinking is behind this.
 
Considering that Simon has quoted direct from the regs what are you basing that statement on?
At what point are you going to change from a Minor works to an EIC?
Not having a go at you, just wondering what your thinking is behind this.

Just got back in, can't believe some of the carp on this, modifying a circuit is what the OP is quoted to do MNW certifate, Trev makes a good point, Simon has quoted the Regs, so like Trev I can't for the life of me understand your reasoning Lenny
 
just a little common sense, if it feels more work than a MWC it probably is. You are the electrician, ultimately the type of cert you produce for the work you've done is down to you. If you're comfortable with your decision to use a MWC (giving your an experienced and competent electrician) then it should be fine. If there's a nagging doubt in the back of your mind that an MWC isn't enough. it probably isn't
 
There's no doubt though Lenny, an extension or alteration to a circuit is on a minor works. A new circuit is an EIC
So as I asked earlier, at what point during this theoretical ring extension are you going to change your cert? adding 5 sockets? 7? 12?
 
just a little common sense, if it feels more work than a MWC it probably is. You are the electrician, ultimately the type of cert you produce for the work you've done is down to you. If you're comfortable with your decision to use a MWC (giving your an experienced and competent electrician) then it should be fine. If there's a nagging doubt in the back of your mind that an MWC isn't enough. it probably isn't

Err...... So what isn't recorded on a MWC that you you think should be?
 
so you added a number of points (actual number irrelevant)to an existing cct, installed in conduit and trunking that you've just installed along a corridor through a wall into say a boiler room for attachment to the buildings BMS panel which will now control the circuit you've just extended. Still MWC?
 
Why is the conduit and trunking relevant?
Is the BMS panel pre-existing or is it a new addition? If it's a new addition then fair enough, I'll be reaching for the EICs but if, for example, it's adding a dozen sockets in an office in dado trunking then it's a MWC
 
so you added a number of points (actual number irrelevant)to an existing cct, installed in conduit and trunking that you've just installed along a corridor through a wall into say a boiler room for attachment to the buildings BMS panel which will now control the circuit you've just extended. Still MWC?

I would have thought Kenny, that if you are installing a supply for a BMS panel then perhaps extending the RFC isn't the way to go. maybe you ought to think about running a dedicated supply, but yes it is still a MNW if you are doing your way i,e, extending the RFC regardless of how many sockets.
 
Thanks for your responses fellas.
Just for info its one double socket extending from RFC in (crappy) trunking for about 3meters max. And another in kitchen 2m max.
So a MWC it is.
Just out of curiosity, as I've never done the following before, would it still be appropriate to issue MWC for a spur of a ring?
Thanks for your input.
 

Reply to ring extension. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
471
  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
157

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top