Ring Final Circuit - spurs only | on ElectriciansForums

Discuss Ring Final Circuit - spurs only in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jun 1, 2020
Messages
624
Reaction score
113
Location
London
I read that it is against the regs that a ring final circuit cannot be just a ring with with spurs off it. In short, a ring must have sockets on it which double up as junctions. I find that hard to believe.
 
Last edited:
A ring can't have more unfused spurs than it has sockets on the ring.
So if there are 10 sockets on a ring then the maximum number of unfused spurs you can have is 10.

Spurs do not have to be taken from sockets, they can be taken from a suitable joint box or from the origin of the circuit.


As always the above refers to the 'standard circuits' as described in the regulations and supporting publications. If you wish to design your own non-standard circuits then you are free to do so, however you would need to fully document the design (as a courtesy to anyone else who has to work on the installation, as defense should anything go wrong, as defense when an EICR is carried out and the non-standard design is flagged up, etc etc)
 
So, a ring can be just a ring of cable - in effect a busbar. Then on this cable j-boxes with spurs off that.

No, it can't, not as a standard ring final circuit.

As I said, a ring can only have as many unfused spurs as it has sockets connected to the ring.

On your ring of cable with joint boxes, if you intend it to be a standard ring final circuit, you cannot have any spurs as you have no sockets on the ring.
 
What would lead you to design a circuit like this?

If you can get one cable to a socket, then you can get two.
It has no financial benefit, as the cable saving is countered by joint boxes and time making those extra joints.
The extra joints also add another point of possible faults.

In technical terms…. This is how a standard socket is. The joint is the terminals on the back of the socket… the “spur” is the internal metalwork between the terminal and the contacts for the plug pins.
 

Reply to Ring Final Circuit - spurs only in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yep! Edit button was disabled by the time I seen it. Hopefully the 15m/15m clarified what I intended 😀
2 3
Replies
36
Views
2K
Very technical :D
    • Like
Replies
9
Views
417

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top