I read that it is against the regs that a ring final circuit cannot be just a ring with with spurs off it. In short, a ring must have sockets on it which double up as junctions. I find that hard to believe.
Last edited:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ring Final Circuit - spurs only in the UK Electrical Forum area at ElectriciansForums.net
So, a ring can be just a ring of cable - in effect a busbar. Then on this cable j-boxes with spurs off that.A ring can't have more unfused spurs than it has sockets on the ring.
So if there are 10 sockets on a ring then the maximum number of unfused spurs you can have is 10.
So, a ring can be just a ring of cable - in effect a busbar. Then on this cable j-boxes with spurs off that.
You can have a ring circuit and have no socket outlets at all if you want.So, a ring can be just a ring of cable - in effect a busbar. Then on this cable j-boxes with spurs off that.
What you save on cable you probably lose more on the junction boxes.Just a thought on this. A ring with jboxes only. The jboxes supply only one socket via a cable approx 2 to 3 metres long. Big saving on cable.
You can have a ring with only j boxes if you want, and yes it's legal as you put it.If this situation arose is it legal. A ring with only jboxes is the point.
Do the junction boxes cost more than the cable you are saving?If this situation arose is it legal? A ring with only jboxes is the point. Or the actual ring cable with no sockets on it.
In #9 you stated big saving on cable.Just a thought on this. A ring with jboxes only. The jboxes supply only one socket via a cable approx 2 to 3 metres long. Big saving on cable.
Reply to Ring Final Circuit - spurs only in the UK Electrical Forum area at ElectriciansForums.net