I read that it is against the regs that a ring final circuit cannot be just a ring with with spurs off it. In short, a ring must have sockets on it which double up as junctions. I find that hard to believe.
Last edited:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ring Final Circuit - spurs only in the UK Electrical Forum area at ElectriciansForums.net
Thx. So OK to have a ring with no sockets on it.If you wish to design your own non-standard circuits then you are free to do so,
The point is a ring without sockets, either with for e.g., having only jboxes or appliances hard wired on the ring. Why the jbooxes are there or why the appliance are hard wired in is not the point. It is a regs point.Why would you hard wire any appliances?
They are designed to be portable, come with a plug.
Give them a socket.
As I said earlier, extra joint boxes and time to install outweigh the cable cost saving.
What about the cost of the joint boxes or are you not going to answer that.The point is a ring without sockets, either with for e.g., having only jboxes or appliances hard wired on the ring. Why the jbooxes are there or why the appliance are hard wired in is not the point. It is a regs point.
I refer you to post 19.What about the cost of the joint boxes or are you not going to answer that.
There are plenty of ring final circuits out there which do not incorporate socket outlets.
Where are we getting. Ring final circuits without sockets outlets have been around since the advent of the ring final.I refer you to post 19.
"There are plenty of ring final circuits out there which do not incorporate socket outlets."
Getting somewhere.
Thx.Ring final circuits without sockets outlets have been around since the advent of the ring final.
The regs don’t state sockets, they will state points.
The regs concerning unfused spurs comes from the load on the spur not being too much for the cable between the ring and the point.
How that cable is joined into the ring is immaterial. Joint box, or back of another point.
That is from memory, as it’s Sunday and I can’t be bothered to look for my book.
I used to believe this too. I don't know if it was included in the 15th or 16th edition, but there's no mention of it in BS7671:2018+Amd2:2022 (at least as far as I can see).A ring can't have more unfused spurs than it has sockets on the ring.
So if there are 10 sockets on a ring then the maximum number of unfused spurs you can have is 10.
Sockets are not for permanently used appliances. They are to be plugged in and out. Permanently wired in appliance need to be hard wired. And that in theory includes a 24/7/365 fridge.
Just a thought on this. A ring with jboxes only. The jboxes supply only one socket via a cable approx 2 to 3 metres long. Big saving on cable.
Reply to Ring Final Circuit - spurs only in the UK Electrical Forum area at ElectriciansForums.net