Hi Gents,

Have an existing circuit at a warehouse where a single 4mm 4core SWA has been used as a Ring Final Circuit. Two cores are in connectors in the back of the socket outlets thus creating a ring. The SWA is therefore the sole means of earthing. There are No banjo's at the sockets and the glands are screwed into galv couplers at the sockets too.
All opinions welcome..
 
Can I ask please what is the mcb type and rating, and the installation method?
I can't picture how the armour gets to the socket earth, but it is Friday ...
 
Can I ask please what is the mcb type and rating, and the installation method?
I can't picture how the armour gets to the socket earth, but it is Friday ...
Piranha earth lock nut behind the brass bush + fly lead = difficult I know but it could be done.
 
The RFC is already a bit of a thing and this is a complication of it. I was going to spell that with a b... but refrained ... As the RFC relies on distributed loads that could be a problem (?). Maybe that could be simulated by alternating outlets across the pairs (if that makes any sense). Then there's the cpc aspect. Armour is fine for that in theory, but will depend on the mcb and Zs.
 
Only problem I see here is no cpcs from the cable glands to the socket earth terminal. Couplers would need removing and gland direct to back box then fit earth washers or earthing nuts.
 
Last edited:
If these are metal clad sockets and the SWA gland is fixed to the galvanised coupler and the coupler is securely fixed to the metal of the back box, then the back box would be acting as the continuation for the cpc across the socket. The connection to the socket earth would be via the metal back box and the accessory screws and any continuity from the contact of the face plate to the back box.

I do not know the current carrying capacity of a metal back box or the security of earthing for the accessory screws (though it seems acceptable for plastic fittings to earth a flush back box) but I would feel that this is not sufficient certainty of current carrying capacity for the earth, even if the continuity is good.

I would prefer fly leads from the armour connection to the socket terminals.
 
Is it me or what is this suggesting?
Not very clear is it, a core would indicate line or neutral, but it might mean a fly lead.

If this was conduit instead of SWA, would banjos be required?
I would still like fly leads at least from back box to socket terminal if not to the conduit/gland.
 
As I understand it, four cores, two to each socket, two to return the ring. (Bit like Hobbit talk) So at last socket the two joined in each socket return to origin, yes?
 
Is it me or what is this suggesting?
It means RFC wired in 4 core cable 4 cores to 1st socket 1 pair connected to anothe pair going to the next socket until you reach the last one where you have 2 L and 2 N, ergo a RFC wired in 4 core.
 

Reply to Ring Final Circuit wired in 4 core SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
278
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
831
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top