steve100
-
I have a query about the Standard A1 Ring Circuit.
It is my understanding that a 2.5mm2 cable is sufficient, this is because the current carrying capacity in a worse case scenario is 20A and because they are run in parallel this gives a total current carrying capacity of 40A and so a 32A MCB will protect the cable. It is also my understand that the 20A figure is taken from Table F6 on page 150 of the green OSG, however there is a worse case scenario (reference method 103) which has a current carrying capacity of only 13.5A for a 2.5mm2 cable. So why is 20A used as the worse case, is it because section H2.3 on page 175 of the green OSG states that the current carry capacity for a A1 ring circuit mustn’t be less than 20A if a 2.5mm2 cable is used?
Hypothetically speaking, can I assume that if I was to increase the cable size to 6mm2 that this would meet the regulation in respect of installation method 103? I do appreciate that there would be other factors to consider but just looking at the logic.
Thanks
It is my understanding that a 2.5mm2 cable is sufficient, this is because the current carrying capacity in a worse case scenario is 20A and because they are run in parallel this gives a total current carrying capacity of 40A and so a 32A MCB will protect the cable. It is also my understand that the 20A figure is taken from Table F6 on page 150 of the green OSG, however there is a worse case scenario (reference method 103) which has a current carrying capacity of only 13.5A for a 2.5mm2 cable. So why is 20A used as the worse case, is it because section H2.3 on page 175 of the green OSG states that the current carry capacity for a A1 ring circuit mustn’t be less than 20A if a 2.5mm2 cable is used?
Hypothetically speaking, can I assume that if I was to increase the cable size to 6mm2 that this would meet the regulation in respect of installation method 103? I do appreciate that there would be other factors to consider but just looking at the logic.
Thanks