Hi, Im new to fault finding, Im on a job where there is no live to live continuity on the ring final circuit which supplys the sockets to the whole house, with new flooring recently installed I cant access the floors, im assuming there are many jbs because its a 1960s property, if I connect one leg of the ring to the cu then go around each socket with a martindale, am I right in saying ill have power to every socket to a point, then at the point I have no power I can split the ring there and convert the final circuit to 2 20amp radials, cheers.
 
If you split the ring at a particular point, you then need to power up the other half to find the next socket, or you’ll be left with the dodgy joint on one of the legs.

Can alternatively be done via dead testing of course.

still likely to be a loose connection behind a socket. Have you actually found them all or is there one hiding in a kitchen cupboard somewhere?
High level bathroom heater point?
Behind a large price of furniture?
 
I think that you need to work out exactly what is wired to where.
there is a possibility that it is not a ring
it could be that there is more than 1 fault.

if you use the method you have suggested, you should then power up the other side of the ring and see what is working.

however, i think if i was doing the job, i would be inclined to remove all the socket faces and test continuity between each socket, to determine on what cable leg the fault actually is.
 
If you split the ring at a particular point, you then need to power up the other half to find the next socket, or you’ll be left with the dodgy joint on one of the legs.

Can alternatively be done via dead testing of course.

still likely to be a loose connection behind a socket. Have you actually found them all or is there one hiding in a kitchen cupboard somewhere?
High level bathroom heater point?
Behind a large price of furniture?
true! Yes all sockets have been known snd checked for any loose connections or breaks
 

Reply to Ring final no continuity on live ends r1 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top