Hello there got a query here - I Have got different results from each of the outlets on some double socket outlets on my R.F.C tests is this normal???? approx 0.2 and 0.5 ??? any help appreciated
 
we were testing continuity of ring final circuits . all seemed ok apart from this .
So it s common with cheap socket to find this result ?

thanks
 
As far as I understand things, the readings taken at each socket should be within 0.05 ohms of each other.

Have you completed all stages of the test (end to end of each conductor, cross connected etc)?
Are you sure that you have cross linked outgoing with incoming conductors?

If all above is ok then I believe that if the readings get progressively higher to a point and then reduce, it could imply a break in the ring - so that you are in effect testing 2 radials.

Alternatively it could be that the sockets with the higher readings are actually spurs?

I would certainly remove socket plates and check for secure connections also.

I wonder what others think as I am quite new to testing also???

Do pls post to say what the problem turns out to be in the end.

Hope this is constructive

D
 
I found a strange thing when I was doing a shed load of periodics and properly doing the R1+R2 test, like many sparks fail to do.... I found with certain cheaper makes of sockets, the readings on the different sides of double outlets were considerably different, so if you try this you may find that one side gives you the reading you should expect, and the other side could give you up to 0.2 ohms more, it's worth a try! Loop tests aren't affected due to the high currents involved....
 
I m sure it was the sockets , because generally it was on the right hand side that we had the higher result .
thanks for you help guys

cheers
 

Reply to ring final results ????? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top