Back to carry on with fault finding/ rectification tomorrow.

Came up with some dodgy results on consumer unit upgrade today.

RFC continuity

r1-r1 = 0.00
rn-rn = 0.00
r2-r2 = 0.13

Looks like I may have an interconnection somewhere along the line. New one for me.

Any tips from you more experienced chaps out there on best way to proceed without having to take every socket outlet off (x18.)

Was going to treat as long radial, draw a plan and use my r2 lead start at CU and work my way round with r1, then rn and see what springs up.

(Have downgraded mcb to 20amp until resolved.)

Thank you

Sy
 
Could be a hidden jb close to cu which I have come across before. Open one socket and check r1. rn and r2 and if readings look good then this is more than likely the problem.
 
0.00 sounds like it is less than one metre from the db and 0.13 about 4m away (you did null before testing didn't you?)
Theoretically the resistance rise on checking the continuity from one leg end to each socket should be less where there is an interconnection then where there is not, but this is probably too subtle for the real world.
[ElectriciansForums.net] Ring interconnect.... Help please
 
The standard figure of 8 test may be the best way forward
The test just as well just be referred to as the interlink test because its possibly its best function
 
(you did null before testing didn't you?)

Yes made sure of that quite a few times, did think at first it was my leads playing up.

I'll keep you posted this could be fun - directly above the CU is a fully tiled bathroom floor, so hoping an offending JB isnt buried under there.

Looking at it again the figure of 8, does look like a better option - thank you.

Think this is just one of those jobs with a few surprises:

- tncs with a ze of 0.44, rang DNO not interested unless over 0.80!
- customer was getting shocks (changing pendant) even with main switch on CU off : original Wylex BS5419 up the spout, in off position getting 230v N - E to ! (long gone in the bin now, nice shiney Hager thats better)

Have a good day

Sy
 
Yes made sure of that quite a few times, did think at first it was my leads playing up.

I'll keep you posted this could be fun - directly above the CU is a fully tiled bathroom floor, so hoping an offending JB isnt buried under there.

Looking at it again the figure of 8, does look like a better option - thank you.

Think this is just one of those jobs with a few surprises:

- tncs with a ze of 0.44, rang DNO not interested unless over 0.80!
- customer was getting shocks (changing pendant) even with main switch on CU off : original Wylex BS5419 up the spout, in off position getting 230v N - E to ! (long gone in the bin now, nice shiney Hager thats better)

Have a good day

Sy

Good luck
 

Reply to Ring interconnect.... Help please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
561
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
936

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top