golfpaul

Changed a cu, doing IR test on the ring comes in at 0.28 l-n, l-e is greater than 200.
Disconnected boiler, neons etc, any ideas?
 
Changed a cu, doing IR test on the ring comes in at 0.28 l-n, l-e is greater than 200.
Disconnected boiler, neons etc, any ideas?

Did you change the CU before testing? what was the IR between N and E? ideas well something still plugged in, TV booster fed from the RFC in the roof space, anyone fitted any shelves plenty more where they came from
 
Washing machine!
Just spotted it, all good now cheers.


Washing machine! .... you mean that big unit sized lump of metal ... can really understand you missing that one..:crowngrin:

If it were a concealed aerial booster or even the ignition on a gas hob then I could understand but a big metal box approx 1m by 0.6m hmmm facepalm! ;)
 
and just to get totally off subject. here's Misia at 10 days old. just starting to hand feed as she had problems. [ElectriciansForums.net] Ring ir very low
 
Loving the nail varnish Tel ...suits you Sir! :)
not my usual colour. i prefer black, but this was for stepdaughters wedding. everything pink apart from the beer. lol. only joking. it's 'er indoors' hand in the photo.
 

Reply to Ring ir very low in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
What @Avo Mk8 suggests crossed my mind. Try an IR test at 500v.
Replies
7
Views
968
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
767
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
667
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
1K
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
492
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks