Hi guys been re -wiring a consumer unit which ive done and had a look behind sockets and ring main looks a mess seems to be spurs off spurs off spurs in some rooms anyone know what the best way forward is? Just put on 20amp breaker , i cant split in board and put on two 20amp mcbs can as they will still be inter connected at places? Or would people reccomend a rewire cables are red black

Cheers
 
Trace the circuit from point to point, also worth drawing it out as you find out what's what. From here you will be able to find the best point to split the RFC and put them on 2 x 20A radials. This way you can be sure of no interconnections etc.
 
Last edited:
Hi guys been re -wiring a consumer unit which ive done and had a look behind sockets and ring main looks a mess seems to be spurs off spurs off spurs in some rooms anyone know what the best way forward is? Just put on 20amp breaker , i cant split in board and put on two 20amp mcbs can as they will still be inter connected at places? Or would people reccomend a rewire cables are red black

Cheers

Hi dude, as above,a test out,with your own drawings,will identify that issue,and the colour of the original wiring is no indication of any need to rewire.

I have many,many clients,who possess and use,installations containing wiring going back to the 1920s'...and as long as it passes inspection and testing...it is just a note :wacko:
 
Hi guys been re -wiring a consumer unit which ive done and had a look behind sockets and ring main looks a mess seems to be spurs off spurs off spurs in some rooms anyone know what the best way forward is? Just put on 20amp breaker , i cant split in board and put on two 20amp mcbs can as they will still be inter connected at places? Or would people reccomend a rewire cables are red black

Cheers


Did you do any checks or testing before changing the CU? by the sounds of it the answer would be no.
 
I did test before but only insulation test. And yes I am only changing board, I am thinking now to disconnect every socket and test each cable to see where it goes and draw it on paper then sort that way...but this will be a long task, any advice?

thanks for the replys
 
Hi guys been re -wiring a consumer unit which ive done and had a look behind sockets and ring main looks a mess seems to be spurs off spurs off spurs in some rooms anyone know what the best way forward is? Just put on 20amp breaker , i cant split in board and put on two 20amp mcbs can as they will still be inter connected at places? Or would people reccomend a rewire cables are red black

Cheers

What makes you think this?

Have you asked your scheme tech support to see what they recommend?
 
I did test before but only insulation test. And yes I am only changing board, I am thinking now to disconnect every socket and test each cable to see where it goes and draw it on paper then sort that way...but this will be a long task, any advice?

thanks for the replys

Why did you say you were rewireing in the op if you aren't?

What tests have you done to establish that the rfc is a mess as you put it?
 

Reply to ring main a mess in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
715
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
321
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top