hi

Done a ring main test,its wired in 2.5 singles and 1mm earth, its a very old install.

continuity readings were 0.35 live 0.35 neutral all good.but the earth is 0.34. does this sound ok to yous??? a know in twin and earth its 1.67 x higher than the conductors.
 
Possible got a parallel path when testing the earth, like a steel conduit or metalclad sockets on steel girders either way the lower the resistance the better if it is a confirmed ring.

The 1.67x is applicable when the earth ratio is correct to the phase conductor but in your case it seems the earth is alot smaller and the expected reading should be 2.5x but as i said it seems you have a parallel path somewhere which if a recognised earth then the undersized earth might not be an issue, not sure if 1mm earth is acceptable with 2.5 ring?
Will leave this open for someone else.
 
Last edited by a moderator:
hi

Done a ring main test,its wired in 2.5 singles and 1mm earth, its a very old install.

continuity readings were 0.35 live 0.35 neutral all good.but the earth is 0.34. does this sound ok to yous??? a know in twin and earth its 1.67 x higher than the conductors.

what were the singles installed in plastic or metal conduit, mini trunking etc
 
hi
they were in metal conduit,got to be a prrallel path

Possibly to late now, but the next time, remove the 1mm or 1.5mm single CPCs and check the continuity of the metal conduit first, then preform the ring contiuity test on the CPCs, just because you do not get the reading as specified by GN.3 OSG etc it does not mean it unsafe.

If the insulation test result were satisfactory and Zs complied, inspection satisfactory I see no need for rewiring circuit.

I would test continuity of the conduit usinfg long lead method working from CCU to wards furthest outlet
 
Last edited by a moderator:

Reply to the thread, titled "ring main earth" which is posted in Periodic Inspection Reporting & Certification on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top