hi

Done a ring main test,its wired in 2.5 singles and 1mm earth, its a very old install.

continuity readings were 0.35 live 0.35 neutral all good.but the earth is 0.34. does this sound ok to yous??? a know in twin and earth its 1.67 x higher than the conductors.
 
Possible got a parallel path when testing the earth, like a steel conduit or metalclad sockets on steel girders either way the lower the resistance the better if it is a confirmed ring.

The 1.67x is applicable when the earth ratio is correct to the phase conductor but in your case it seems the earth is alot smaller and the expected reading should be 2.5x but as i said it seems you have a parallel path somewhere which if a recognised earth then the undersized earth might not be an issue, not sure if 1mm earth is acceptable with 2.5 ring?
Will leave this open for someone else.
 
Last edited by a moderator:
hi

Done a ring main test,its wired in 2.5 singles and 1mm earth, its a very old install.

continuity readings were 0.35 live 0.35 neutral all good.but the earth is 0.34. does this sound ok to yous??? a know in twin and earth its 1.67 x higher than the conductors.

what were the singles installed in plastic or metal conduit, mini trunking etc
 
hi
they were in metal conduit,got to be a prrallel path

Possibly to late now, but the next time, remove the 1mm or 1.5mm single CPCs and check the continuity of the metal conduit first, then preform the ring contiuity test on the CPCs, just because you do not get the reading as specified by GN.3 OSG etc it does not mean it unsafe.

If the insulation test result were satisfactory and Zs complied, inspection satisfactory I see no need for rewiring circuit.

I would test continuity of the conduit usinfg long lead method working from CCU to wards furthest outlet
 
Last edited by a moderator:

Reply to ring main earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
434
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
935
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
892

Similar threads

In addition, can you show the junction box with the cover off? Isolate the supply first, obviously. It sounds strange, what you’ve described at...
Replies
2
Views
169
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top