J

john h owen

working out by calculation the end to end resistance of a ring main given L = 65m cables = 2.5 mm and 1.5 mm and mohms/m = 7.41 and 12.10 respectively at 20 degress. and cables are 70 degress thermoplastic bunched in trunking and conduit.Cpc in the same trunking and conduit

Would you have to use the bunched 1.2 factor when calculatring the end to end resistance of the cables?
 
working out by calculation the end to end resistance of a ring main given L = 65m cables = 2.5 mm and 1.5 mm and mohms/m = 7.41 and 12.10 respectively at 20 degress. and cables are 70 degress thermoplastic bunched in trunking and conduit.Cpc in the same trunking and conduit

Would you have to use the bunched 1.2 factor when calculatring the end to end resistance of the cables?

You apply factors in order to determine the CSA of cable to be used.

The reading you will get from measuring the end to end resistance of 75m of 2.5mm T&E will be the same whether it was bunched or not.
 
Then what if his resistance readings + ze were to high for the given circuit breakers max zs, would he not have to change cable size?
 
if he sticks to the rules for a ring main size then he shouldnt really go over , unless there was a high Ze, in which case
larger cpc could be run

an rcd gives a zs of 1667 ohms (although brb values should be met)
 

Reply to ring main end to end resistance. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top