nickblake
A little while ago i put a post on a thread regarding a periodic i carried out on a small bungalow where there was no continuity on all three conductors of the ring and testing showed a very high Zs reading 2.64 althought the insulation was ok , well today ive been back to the property to investigate , so i split the ring into 2 at the CDU ,it appeared to be radials during the testing but i had one of them feelings you know the ones , so started off doing an R1R2 from the CDU around the ring so first socket 0.27 great then increased up to 0.47 then went to 1.34 , removed socket and found some loose connections then after that nothing , so started on the other leg at the CDU working round till nothing so it was up in the loft followed cables round you could see the ring , found a JB which i will add was wired put it this way diffrently ring added for a utility room joined together off the ring wires split up added 2 new legs installed new circuit for utility easy job as good accesss to CDU , still no cont inuity so it was go round eaach leg feeling the cable all appeared to be ok till i got to one of the open circuit sockets and it just pulled up choped in half , half way up the wall it went to an unused socket so cut out the other leg joined with a jb re tested and 0.51 0.51 .074 .0.24 /200 200 200 . 0.68 Zs all i can say is happy days found the fault and all ok yipeee