hi all, Got called to a job tonight, ring main blowing fuses, did the usual and disconnected all equipment and did insulation test and got a result 0.01 Meg ohms between between live to earth, and live to neutral, so then did a continuity but got open circuits on all test, i joined live&neutral together and insulation tested it again to check there was nothing i missed to disconnect even thought I'm 100% sure there was nothing, i have to back tomorrow to try and sort it out but could any give me any pointer as i could understand why the open circuit.

thanks.
 
Last edited by a moderator:
is it blowing a fuse mcb or tripping the RCD , did you do a ring continuity , and its open circuit or a continuity of the conductors to earth ie live to earth continuity , do a live to earth continuity see if you get a reading if you do test at each socket and see where you get the lowest reading and then check that socket , if the fault is located re do the IR but do it a 250 volts first
 
it the old push in fuses, i did a continuity of conductors to earth and it was open circuit on all legs joined (Live & Live joined, Netural & Netural joined to earth) but 0.01 Meg ohm on insuation
 
Well maybe it falls between 2,000 & 10,000 ohms?

I doubt it though.

0.01 Megohms is, as you say, 10,000 Ohms. If reading to two decimal places then anything above 0.005 Megohms would read 0.01 Megohms and anything below presumably 0.00 Megohms. If that assumption is correct then it is reading at least 5,000 Ohms between line and cpc or whatever was being measured..
 
Well done.

Reminds me of a nuisance client I had last year where I carried out a periodic and had the same thing. He was an electronics engineer and refused to believe you could have an open circuit and a below 1 megaohm at the same time. I ended going back to redo the tests with him watching, turned out to be water penetration in an outside light (it was snow at the time). He withdrew his complaint.
 
thanks

snow can cause so many troubles
if snow can close half the schools, bring the country almost to a grinding halt, who are we to compain about an occassional trip caused by snow in the electrics
 

Reply to Ring Main Fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
732
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top