When I turn a load on on the ring main it trips the rcd, is this due to there being a fault between neutral and cpc?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ring Main Fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
When I turn a load on on the ring main it trips the rcd, is this due to there being a fault between neutral and cpc?
Have you got the neutrals in the right bar in the CU?
trips out on all socketsdoes the RCD trip on all socket outlets, or just 1 of them? could be a N/E reversal.