Hi guys, looking for some advice on the following problem.

So heres the issue:

I was called round to a house because this womens sockets were tripping her RCD, at first it was occasionally, and by the time she a had called me the RCD would not stay on if the ring main was energised.

So i started to investigate, turns out we were dealing with a low reading 20ohms between live and earth (insulation resistance) in the circuit. The problem leg was found and fixed. Now the real issue, on this supposed 'ring' im not getting any continuity on my phase conductors (live and neutral) So again i started to delv deeper into my inspection, i found:

-The kitchen was a recent addition to the home, and sockets appear to spurred from other sockets, and im almost certain there is a joint left in the wall somewhere.
-When attempting a Figure of 8 continuity check, reading at socket outlets were all over the place ranging from 1.08ohms to 2.67ohms, i was hoping to trace out the break using this, but reading were so scattered.
-It then got me thinking that this circuit may actually be two radials, just joined together at the board and put into a 32amp breaker? Bear in mind though that the cable is 2.5mm

Im going back to the house today to try get to the bottom of this, first by testing the circuit from fresh, noting results, then going to try and map out exactly what leg goes where, and check every bit of the circuit for defects. Bear in mind guys, this circuit appears to have had alot of tampering, ie breaking into to and spurring etc.

Any advice from you guys would be great.
 
Maybe set up for r1 r2 test on each leg at the board, make sure u have good readings at every outlet on the circuit, then bang them on a 20amp mcb
 
suggest taking 1 leg out then finding out which sockets are powered. then repeat for 2nd leg. that should confirm if you have 2 radials and if the ring has been split. solution then is to repair the ring, or split it into 2 20A radials.
 
Got a similar problem myself at the moment and the house in question does have 2 spurs in a 32A breaker. Not got to the bottom of the "fault" as yet, but very frustrating that the "recent" changes to the house, don't have any test results nor certificates!

Good luck
 

Reply to Ring main problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

https://www.amazon.co.uk/gp/product/B08CJ3VC79/ref=ppx_yo_dt_b_asin_title_o05_s00?ie=UTF8&psc=1 I use this, current clamps go round each outgoing...
Replies
3
Views
714
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top