In relation to an earlier thread.
I need to quote for tree hugger type house, super duper insulation in cavities (some type of expanded foam + other stuff)
anyhow the spec is quite clear, allowance and cable size must be allowed for in your quotation (insinuating cable size is not standard) ..blah blah blah, without actually saying what size,
For the cooker, shower etc its quite straight forward when knowing the exact load on a said circuit...for instance I calculate the 2.5kw water heater needs to be wired in 6mm...
But what size a ring main, where the load is unknown, if on full load of 32amp I get a stupid size of 10mm, allowing for half i need 6mm, yet I know its very unlikely the load will exceed 10 amps, even in kitchen no more than 20 amps, split on one radial and one ring main...so what size cable for ring mains?
I need to quote for tree hugger type house, super duper insulation in cavities (some type of expanded foam + other stuff)
anyhow the spec is quite clear, allowance and cable size must be allowed for in your quotation (insinuating cable size is not standard) ..blah blah blah, without actually saying what size,
For the cooker, shower etc its quite straight forward when knowing the exact load on a said circuit...for instance I calculate the 2.5kw water heater needs to be wired in 6mm...
But what size a ring main, where the load is unknown, if on full load of 32amp I get a stupid size of 10mm, allowing for half i need 6mm, yet I know its very unlikely the load will exceed 10 amps, even in kitchen no more than 20 amps, split on one radial and one ring main...so what size cable for ring mains?