Started on a job today, where the customer wanted a new consumer unit to 17th edition standards, and a check over of Electrics which they know is something weird.
Started doing some testing before i ripped it all out tomorrow, and found Circuit 1 and Circuit 2 supplying the main ring, only dead when both fuses are pulled, further investigations into ring found the two wires that were in circuit 2 were not the ring, but doing a continuity test found the ring was the live from circuit 1 and one of the lives from circuit 2.
Another find was the third wire was a positive reading with one of the legs of the ring, but not both.
I hope this all makes sense, because i was struggling at start.
In summary 3 wires on two circuits we shall call R1, R2 and R3 for ease, R1 and R2 have continuity, also R1 and R3 have continuity, but R2 and R3 don't, as I want to seperate these whats the quickest way to investigate this problem.
 
wired in t and e 3 cables one to circuit 1 and the other two to circuit 2 tested using my megger mft 1552
 
Probably best to start from scratch, disconnect ALL cables and continuity test to find out where they go it will be difficult on your own try and get a mate to help
 
R1 and R2 have continuity, also R1 and R3 have continuity, but R2 and R3 don't
Strictly speaking this isn't possible. If A is connected to B and B to C, then by definition A is connected to C. You don't mention what the resistance readings are, but I wonder whether you are reading through some connected loads that are bridged between the circuits, or a high-resistance fault between the circuits? Perhaps the resistance from R2 to R3 (confusing terminology!) is just too high for your tester to give an indication on the continuity range but would show up as the sum of the other two if tested using a higher range. Also, if anything energised is interconnected as well, the tester might give peculiar readings on the circuits that you think are isolated. Agree with above, need to break down into manageable chunks.
 
What size breakers are circuit 1 and circuit 2. Re-reading the OP I think you might have a ring and a spur with 1 leg of the ring in the wrong breaker. If you are talking about just the lives (red/brown) then R1 - R2 you should have continuity and they should be in the same breaker, R3 is your spur (maybe).
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ring main Snags
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
Dazzol2009,
Last reply from
ifindoubtdont,
Replies
9
Views
1,400

Advert

Back
Top