Dazzol2009

Started on a job today, where the customer wanted a new consumer unit to 17th edition standards, and a check over of Electrics which they know is something weird.
Started doing some testing before i ripped it all out tomorrow, and found Circuit 1 and Circuit 2 supplying the main ring, only dead when both fuses are pulled, further investigations into ring found the two wires that were in circuit 2 were not the ring, but doing a continuity test found the ring was the live from circuit 1 and one of the lives from circuit 2.
Another find was the third wire was a positive reading with one of the legs of the ring, but not both.
I hope this all makes sense, because i was struggling at start.
In summary 3 wires on two circuits we shall call R1, R2 and R3 for ease, R1 and R2 have continuity, also R1 and R3 have continuity, but R2 and R3 don't, as I want to seperate these whats the quickest way to investigate this problem.
 
Probably best to start from scratch, disconnect ALL cables and continuity test to find out where they go it will be difficult on your own try and get a mate to help
 
R1 and R2 have continuity, also R1 and R3 have continuity, but R2 and R3 don't
Strictly speaking this isn't possible. If A is connected to B and B to C, then by definition A is connected to C. You don't mention what the resistance readings are, but I wonder whether you are reading through some connected loads that are bridged between the circuits, or a high-resistance fault between the circuits? Perhaps the resistance from R2 to R3 (confusing terminology!) is just too high for your tester to give an indication on the continuity range but would show up as the sum of the other two if tested using a higher range. Also, if anything energised is interconnected as well, the tester might give peculiar readings on the circuits that you think are isolated. Agree with above, need to break down into manageable chunks.
 
What size breakers are circuit 1 and circuit 2. Re-reading the OP I think you might have a ring and a spur with 1 leg of the ring in the wrong breaker. If you are talking about just the lives (red/brown) then R1 - R2 you should have continuity and they should be in the same breaker, R3 is your spur (maybe).
 

Reply to Ring main Snags in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
715
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
817
In addition, can you show the junction box with the cover off? Isolate the supply first, obviously. It sounds strange, what you’ve described at...
Replies
2
Views
136

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top