Ring off a ring ! Help please | on ElectriciansForums

Discuss Ring off a ring ! Help please in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 3, 2019
Messages
2
Reaction score
5
Location
Skegness
Hi, I know you can’t put a ring off a ring, you should join a cable in the back box of a socket, take it to your new socket, then continue the ring until you get back to your original socket

But I don’t know the reasoning why you can’t make a figure of 8 ring main if you like,
Could someone help me please
Many thanks
 
It puts a large load at one point instead of distributing the total load reasonably around the ring, with the possibility of overloading one leg if not near the centre of the ring. Similar to taking a single unfused spur in 4 or more sq.mm off to feed lots of sockets or, say, a cooker or shower.
 
Last edited:
Hi Jordan and welcome.
As per @M-Ty, its a point load on the original ring with a bunch of outlets. So you’d need to connect it by a 13A fuse. If you preserved the original ring the 32A rating extends to the new bit, as long as the new ring meets earth loop impedance limits.
 
Mathematically I think it's no different to a lollipop circuit but testing would be a pain in the rear and I can't think of a single instance where extending the ring wasn't the easiest option.

I'll be honest I can't see the need or use for it.
 
Also why would you wanna do that.
If I’m adding 3/4 sockets of ring I usually come off to a unswitced spur then radial to power points,obviously in local area.some of these new houses are a mare to add anything new,ie: chipboard floors,Also your not the disturbing the ring as such,
 
A diagram to show the potential for overload as described by M-Ty using some possible current loads (obviously chosen to overload the cable)
You would have to work at it to overload but it is more likely and you would not need to overload the MCB to do it.
[ElectriciansForums.net] Ring off a ring ! Help please
 
Hi, I know you can’t put a ring off a ring, you should join a cable in the back box of a socket, take it to your new socket, then continue the ring until you get back to your original socket

But I don’t know the reasoning why you can’t make a figure of 8 ring main if you like,
Could someone help me please
Many thanks
First of all have you tested the circuit you wish to extend are the readings acceptable
 
Although not dangerous in theory if there were a break in one of the legs after the cross over this would not show on an end to end test on a c.u. or d.b. therefore leaving one leg liable to overload. Or so my understanding leads me to believe.
 
Thanks guys! I just passed my AM2 and completed my NVQ, after telling my dad he’s extended the ring in the wrong way, he still knows best! I just didn’t know the reasoning behind it!
Thanks for your help and welcoming me onto this site

....It always touches me,when i see a family sharing such personal troubles...;)
 
Thanks guys! I just passed my AM2 and completed my NVQ, after telling my dad he’s extended the ring in the wrong way, he still knows best! I just didn’t know the reasoning behind it!
Thanks for your help and welcoming me onto this site
Get you dad signed up on here quick.
 

Reply to Ring off a ring ! Help please in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
672
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top