Just done some small alterations to a training room it's a 4mm radial in dado trunking that was already there there is 7 pcs to be plugged into circuit I suggested making it into a ring but the engineer were working for says its ok I thought all pcs had to be on ring du to high integratity earthing
 
Ok Kas so if I or should I say we run a 4mm earth back to db connected in separate earths of course this would solve the issue just for the record though what spark would disconnect an earth of a live circuit any way and be on the end of the earh leakage from the pcs always baffled me this one
 
Computers can generate leakage currents that can cause RCD tripping problems as they can also have functional earthing requirements that suppress noise on the computer supply.
If the leakage current is high, say with ten or more computers, then the cpc should be doubled and, for a radial run, in a ring, but the live conductors do not need to be in a ring, it is only to ensure that the cpc connection is not broken by accident (i.e. high integrity earthing).
The cpcs should also be terminate in the accessories separately.
 
Last edited:
I didn't write the regs lol, personally I'd of put them on a ring, I've worked on contracts where they've specced 4mm rings as standard so I'd of gone with your suggestion for the sake of a bit a cable and you would of then achieved the high integrity earthing as well, but I can see no reg where computers have to be on a ring, it could be a radial with 2 cpc's with one being a conduit or trunking.
 
all you need to do is use both earth tags on each socket, then from the last socket on the radial, take a 4.0mm single g/y back to DB. terminate in a different hole.
 
no problems with a radial only, the ringing of the cpc is belt and braces in case of a cpc snapping off at a terminal. you can measure the earth leakage with a clamp meter if you need to, a pc has a typical leakage of around 3mA.
 

Reply to Ring or radial in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
600
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top