It is not coming into contact with the earth leakage that is the main problem, although that is the effect we are trying to control, it is ensuring that the piece of equipment is continuously connected to the MET.
Because the suppression filters, SM power supplies, etc., generate a potential on the earth that can deliver over 10mA there is a risk of harm to someone touching any exposed conductive parts of the equipment if the equipment is not earthed, I know a lot of the desk IT kit is double insulated now, but there is a still a reasonable amount that is not and more in server rooms.
Also the lack of an earth will render the suppression useless as the leakage current is from a functional earth and without it the transients have nowhere to go.