Just done some small alterations to a training room it's a 4mm radial in dado trunking that was already there there is 7 pcs to be plugged into circuit I suggested making it into a ring but the engineer were working for says its ok I thought all pcs had to be on ring du to high integratity earthing
 
It is not coming into contact with the earth leakage that is the main problem, although that is the effect we are trying to control, it is ensuring that the piece of equipment is continuously connected to the MET.
Because the suppression filters, SM power supplies, etc., generate a potential on the earth that can deliver over 10mA there is a risk of harm to someone touching any exposed conductive parts of the equipment if the equipment is not earthed, I know a lot of the desk IT kit is double insulated now, but there is a still a reasonable amount that is not and more in server rooms.
Also the lack of an earth will render the suppression useless as the leakage current is from a functional earth and without it the transients have nowhere to go.
 
It is not coming into contact with the earth leakage that is the main problem, although that is the effect we are trying to control, it is ensuring that the piece of equipment is continuously connected to the MET.
Because the suppression filters, SM power supplies, etc., generate a potential on the earth that can deliver over 10mA there is a risk of harm to someone touching any exposed conductive parts of the equipment if the equipment is not earthed, I know a lot of the desk IT kit is double insulated now, but there is a still a reasonable amount that is not and more in server rooms.
Also the lack of an earth will render the suppression useless as the leakage current is from a functional earth and without it the transients have nowhere to go.
its effectively an earth screen....dumping stray...
 
Personally i wouldn't have more than 5 PC workstations on any one circuit!! Having RCD protection on PC/IT work station circuits, is just asking to loose any unsaved data, but it still seems all too common to do so!! lol!!

High integrity earthing is specified for a purpose, and something that the OP's Engineer should have been aware of, and suggested a dual/ringing of the CPC
 

Reply to Ring or radial in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
602
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top