I have just tested ring circuit and found that the cpc has a break in it.
What is the best way to find out where the break is and what action should i take if not found.:confused:
 
1, test between sockets starting from consumer unit (especially if dado rail present) until no continuity.
2, use a TDR (time domain reflectometer) gives you a reasonable distance where the break is from the point of testing.
 
If the L and N are intact it's almost certain to be a break where terminated in a socket....if there are not too many sockets on the circuit it can be just as easy dropping them for a look see until you find the offender,rather than testing...of course if there are lots of points or they are dfficult to remove testing is the way to go.
 
If the L and N are intact it's almost certain to be a break where terminated in a socket....if there are not too many sockets on the circuit it can be just as easy dropping them for a look see until you find the offender,rather than testing...of course if there are lots of points or they are dfficult to remove testing is the way to go.

Good advise
Its easy to dive into something like this, with tester in hand and brain spinning and end up virtually doing the above anyway
 
I would disconnect one of the cpc's from the CU, then using a long lead, test continuity from the MET to each socket ( either to screw or use a socket adaptor ). As you go round you will eventually find one that doesn't bell out, it will either be that socket, the socket you tested prior or the cable between them. Quick and simple and no removal of socket fronts until you pinpoint the fault. Once you have rectified check end to end again just to make sure you only had a single break.
 
Last edited by a moderator:
Thanks to all for the advice. However, the L and N are intact and after checking firstly behind every socket, all earths appear to be connected ok. Also disconnected one earth at consumer unit and identified sockets with that earth. Then tried other end and identified sockets with that earth.
During these checks it was also apparent that some were single wire or spurs but only found one with three wires feeding a spur.
 
Get the line and cpc from one leg and connect them together at the CU. Using your plugtop attachment for your tester, low-ohm test between line and cpc - the further away you get, a higher reading you should get, until eventually you get no continuity. Between the highest reading and no cont is where your fault is. If it isn't apparent which way they are wired, do the same on the other leg (disconnecting the first leg) and perform the same test on the other sockets. Split the ring between the two highest reading sockets, put each leg in a 16A breaker, bish bash and indeed bosh.
 
Get the line and cpc from one leg and connect them together at the CU. Using your plugtop attachment for your tester, low-ohm test between line and cpc - the further away you get, a higher reading you should get, until eventually you get no continuity. Between the highest reading and no cont is where your fault is. If it isn't apparent which way they are wired, do the same on the other leg (disconnecting the first leg) and perform the same test on the other sockets. Split the ring between the two highest reading sockets, put each leg in a 16A breaker, bish bash and indeed bosh.

Thanks Rocker. Thats just the way I tested and identified the sockets on each leg of the earth.
To split the ring (ie the L and N) I take it this will need to be under the floor (upstairs sockets) and not possible behind a socket?
 
.
To split the ring (ie the L and N) I take it this will need to be under the floor (upstairs sockets) and not possible behind a socket?

No , it can be split at a socket. If you are struggling to find the break ie it is not a bad termination at a socket you should be able to narrow it down to between two points then try and trace the approx route out and notice where pictures have been hung on walls, curtain poles, picture rails, even skirting boards etc have been fastened, particularly if an area has been recently decorated.
 

Reply to Ring testing - cpc fault - help please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top