2, use a TDR (time domain reflectometer) gives you a reasonable distance where the break is from the point of testing.
If the L and N are intact it's almost certain to be a break where terminated in a socket....if there are not too many sockets on the circuit it can be just as easy dropping them for a look see until you find the offender,rather than testing...of course if there are lots of points or they are dfficult to remove testing is the way to go.
Get the line and cpc from one leg and connect them together at the CU. Using your plugtop attachment for your tester, low-ohm test between line and cpc - the further away you get, a higher reading you should get, until eventually you get no continuity. Between the highest reading and no cont is where your fault is. If it isn't apparent which way they are wired, do the same on the other leg (disconnecting the first leg) and perform the same test on the other sockets. Split the ring between the two highest reading sockets, put each leg in a 16A breaker, bish bash and indeed bosh.
.
To split the ring (ie the L and N) I take it this will need to be under the floor (upstairs sockets) and not possible behind a socket?