Working on a RFC today and its had a stand alone RCD added previously which is installed outside of the 3036 fuse board.

When testing ring continuity and R1R2 would taking the conductors out of the RCD then joining them be the prefered method or taking 2 readings, one from the fuse board to the RCD then the other from the RCD out round the ring?

I know the values will be the same either way but just wanted to see how others would approach it.
 
The only place you would get ring continuity would be on the outgoing side of the RCD not from the DB as upto the RCD from the DB is a radial circuit.
 
Last edited:
I've been lost in translation on this one. What has the RCD got to do with testing a ring final? Why can't you just do a simple CoRFC test at the board?
 
I would take the reading from the top side of the RCD and call that my reading, then I would measure the link from the board to the RCD seperately and put this reading in 'notes'.
 

Reply to Ring testing when stand alone RCD is used. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
343

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top