I've got a feeling that the OP might be cross-connecting at the socket so that he only has to isolate the RFC at the MCB, instead of the whole installation.
If this was the case and he was working on a TN-C-S system, the Neutrals and CPCs of the ring final are basically connected together.
If when testing your R1 + R2, you wouldn't know if you had a neutral/earth swap at the socket, because you'ld get a reading either way.
And lets not pretend that people never just isolate the circuit that they are working on
Then, even if you isolate the whole of the installation correctly at the main switch (both poles), you could still have the same problem (as above) if there were a N/E fault on another circuit that you didn't know about.
That's probably why cross-connecting at the socket isn't a given method in any of the books - or if it is, I haven't come across it
, and I certainly wouldn't do it.