Gnasher
-
Hi all can you help to settle a argument.
Situation
2 x 4mm in the top of a 32mm. MCB
Option 1
This indicates to me that it is either 2 radials in the same MCB, or a 4mm ring.
A ring continuity test should be carried out to prove that a ring exists or it is 2 radials.
If a ring exists carry on with ring tests. If 2 radials this should be raised further investigation required to identify if an incomplete ring is present, (fault) or it is indeed 2 radials from the same MCB (fault)
option 2
Doesn't matter if it is a ring or not as 4mm is good for 32A carry on and test.
Please vote option 1or 2
my option is 1
yes there are 2 conductors in the MCB
for this posting 4mm conductors throughout the circuit is not an issue.
Quite right should read my post prior to submitting, it's 2conductors. I agree with your option 2 comment I posted this as I am feed up fighting my corner I am looking for a bit of support in my argument
Situation
2 x 4mm in the top of a 32mm. MCB
Option 1
This indicates to me that it is either 2 radials in the same MCB, or a 4mm ring.
A ring continuity test should be carried out to prove that a ring exists or it is 2 radials.
If a ring exists carry on with ring tests. If 2 radials this should be raised further investigation required to identify if an incomplete ring is present, (fault) or it is indeed 2 radials from the same MCB (fault)
option 2
Doesn't matter if it is a ring or not as 4mm is good for 32A carry on and test.
Please vote option 1or 2
my option is 1
yes there are 2 conductors in the MCB
for this posting 4mm conductors throughout the circuit is not an issue.
Quite right should read my post prior to submitting, it's 2conductors. I agree with your option 2 comment I posted this as I am feed up fighting my corner I am looking for a bit of support in my argument