I was on a site today in central London. The building had boilers in the basement, and then two risers, each with a stairwell for access over eight floors.
I was called as the lights don't work in the stairs. After some investigation and getting pretty sweaty, I found the wires had been cut and some of the conduit removed. At the bottom of riser one, where the access is from the boiler room, a new light had been fitted.
The new light was an emergency light, and had a cpc run to it. In the old lighting system, there was no CPC, the light fittings were very old, with ceramic connectors.
I ran a 500v IR test, all the old cable was fine. It looks like the lights had been run as a ring, which (of what was left) was still OK.
My first concern was, why has this been excluded? Is it because it had no CPC? It looks like the lights are earthed to the conduit. Is this acceptable? Or was it excluded due to lack of CPC and whoever excluded it couldn't be bothered (or wasn't contracted to) to replace the old cable and light fittings.
I've advised that the old light fittings should be replaced with double insulated fittings, and new wiring to include a CPC, before being integrated into the new light at the bottom. Is this correct advice, or unnecessary work?
Thanks in advance!
I was called as the lights don't work in the stairs. After some investigation and getting pretty sweaty, I found the wires had been cut and some of the conduit removed. At the bottom of riser one, where the access is from the boiler room, a new light had been fitted.
The new light was an emergency light, and had a cpc run to it. In the old lighting system, there was no CPC, the light fittings were very old, with ceramic connectors.
I ran a 500v IR test, all the old cable was fine. It looks like the lights had been run as a ring, which (of what was left) was still OK.
My first concern was, why has this been excluded? Is it because it had no CPC? It looks like the lights are earthed to the conduit. Is this acceptable? Or was it excluded due to lack of CPC and whoever excluded it couldn't be bothered (or wasn't contracted to) to replace the old cable and light fittings.
I've advised that the old light fittings should be replaced with double insulated fittings, and new wiring to include a CPC, before being integrated into the new light at the bottom. Is this correct advice, or unnecessary work?
Thanks in advance!