Just been to see a customer who's mcb trips out rcd every time switched on first time it happened was in the middle of the night

tested insulation resistance and failed quite dramatically he said he's had a problem with mice so in my mind I'm thinking theres a half chewed cable somewere under the floor does any one know of a simple method of tracing the damaged segmant or is it a case of ripping the floor up until I find it ?

or could it be somthing completley different?
 
located faulty link in the ring seems to be buried in concrete floor, replaced with temp cable to get up and running all works and tests ok IR >300M Ohms need a return visit to replace temp leg all in all time spent in total inc materials I reckon 5hrs +ÂŁ10 for cable and lifting of certain polished floor boards ÂŁ135.

Would you say this is a reasonable cost?
 
Hi Drywax,

Do you know the length of the cables and routes? Normally not I guess, so a case of investigation which is expensive for the customer in time and money..

The only thing I can suggest is to breakdown the ring final circuit into its legs and isolate which section by testing which is ok if it is not an intermittant fault.

If it was a break in the conductors I was told of a method for finding breaks in audio cable using a capacitance meter which could pinpoint the break at its distance from the test point, you have to know which conductor is broken and which is good. Then test at each end, divide the capacitance values giving a fraction and then multiply it by the total length of the cable.I havent tried this but it sounds believable.

Hope this helps,
Best wishes,

Rex
 
Yeah may try it some day rext thanks although it may take a week for what you said to sink in :)

I broke the ring in half IR both legs

found the bad half of the leg

then broke that leg in half did another IR

and continued until I found the bad link

certainly learnt a lot and as electrical cabling is a new field to me goes to prove no matter how much you have in the certificate tray you can't put a price on experience
 
Hi Drywall,

Halving the ring is probably the quickest way but as you say it does still take time.

Hope the householder is going to set some traps for the mice!

Best wishes

Rex
 
Hi Drywax,

Do you know the length of the cables and routes? Normally not I guess, so a case of investigation which is expensive for the customer in time and money..

The only thing I can suggest is to breakdown the ring final circuit into its legs and isolate which section by testing which is ok if it is not an intermittant fault.

If it was a break in the conductors I was told of a method for finding breaks in audio cable using a capacitance meter which could pinpoint the break at its distance from the test point, you have to know which conductor is broken and which is good. Then test at each end, divide the capacitance values giving a fraction and then multiply it by the total length of the cable.I havent tried this but it sounds believable.

Hope this helps,
Best wishes,

Rex

This works, but in real life- not a chance. for instance, I put in 8 meters of 2.5 today to get to a socket a couple 0f meters away from the origin.When dealing with meaured values you need to accurate with cable lengths, its just not possible unless you can see the run, in that case you probably could see the fault.
 
Hi Jason,

Thanks, very good point, have never tried it and remember reading it somewhere or someone mentioning it. It seemed worthwhile mentioning it as it might have helped a bit.
Finding breaks in cables that are concealed and of which the lengths are not known is difficult. I know someone is going to mention that if we know the CSA then we can reasonably know the resistance per metre from page 166 of the On Site Guide however even this can be a bit hit and miss in the real world.
I guess you cant beat the MK1 eyeball!

Best wishes,

Rex
 
Hi Jason,

Thanks, very good point, have never tried it and remember reading it somewhere or someone mentioning it. It seemed worthwhile mentioning it as it might have helped a bit.
Finding breaks in cables that are concealed and of which the lengths are not known is difficult. I know someone is going to mention that if we know the CSA then we can reasonably know the resistance per metre from page 166 of the On Site Guide however even this can be a bit hit and miss in the real world.
I guess you cant beat the MK1 eyeball!

Best wishes,

Rex
your right mate- even if you know where the fault is, you still gotta lift the boards to replace the section of cable------
 

Reply to Rodent problems in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
132
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
914
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Norcal - thanks, belatedly. 'Tis the season when I don't get anything done, even though this project is near the top of the list. Per your...
Replies
7
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top