hi all any advice on the following scenario much appreciated. I have taken on a rewire from another electrician whos personal circumstances mean he cant finish the project. Majority of the first fix has been completed including the repositioning of the DB. The original DB was situated inside the kitchen base units adjacent to the meter and cut out. I can see why the DB is being moved as it isnt the most accesible of places and a new utility room is being created which is much more suitable. However it is the routing of the new ‘ tails’ that im not 100% comfortable with.

25mm double insulated tails along with a 16mm CPC have been run at low level behind the new kitchen base units before rising up in a PVC trunking to ceiling height. They then run approximately 8mtrs through the joist before again dropping down in a PVC trunking to what will be the new DB position. At no point are they buried in a wall. Personally i would have used 16mm2
T&E but the ceiling is now boarded and skimmed so the customer and builder is very reluctant to drop the ceiling and allow me to do this. The intention is to provide our own overcorrect protection at the origin so as not to be solely relying on the 100a DNO fuse.

Ive searched varies threads looking for an answer or advice so apologies if this has been done to death. Can anyone point me in the right direction of where to look in the regs or offer any other advice
 
hi all any advice on the following scenario much appreciated. I have taken on a rewire from another electrician whos personal circumstances mean he cant finish the project. Majority of the first fix has been completed including the repositioning of the DB. The original DB was situated inside the kitchen base units adjacent to the meter and cut out. I can see why the DB is being moved as it isnt the most accesible of places and a new utility room is being created which is much more suitable. However it is the routing of the new ‘ tails’ that im not 100% comfortable with.

25mm double insulated tails along with a 16mm CPC have been run at low level behind the new kitchen base units before rising up in a PVC trunking to ceiling height. They then run approximately 8mtrs through the joist before again dropping down in a PVC trunking to what will be the new DB position. At no point are they buried in a wall. Personally i would have used 16mm2
T&E but the ceiling is now boarded and skimmed so the customer and builder is very reluctant to drop the ceiling and allow me to do this. The intention is to provide our own overcorrect protection at the origin so as not to be solely relying on the 100a DNO fuse.

Ive searched varies threads looking for an answer or advice so apologies if this has been done to death. Can anyone point me in the right direction of where to look in the regs or offer any other advice
These "double insulated tails" the should be described as Insulated and Sheathed tails, I know I'm pedantic
 
Maybe there isnt. I may be looking for one because its not how i would have done it myself. On the surface it all seems ok. Its just the length of those tails and more the fact that they run through the joists like they do
6181Y conductors are no different to T&E with regards to the construction of the insulation and sheathing.
 
hi all any advice on the following scenario much appreciated. I have taken on a rewire from another electrician whos personal circumstances mean he cant finish the project. Majority of the first fix has been completed

I know its been covered before here, but have you covered your botty, taking on the completion of someone else's installation?
 

Reply to Routing of meter tails in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
Yeh that’s my thinking. I have to supply the box so can order a bigger 3 phase option to give myself a bit more room
Replies
3
Views
838
I see no issue with this, it sounds like a relatively normal installation. The use of insulated and sheathed cables inside steel trunking is a...
Replies
5
Views
265
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top