S-type RCBOs | Page 2 | on ElectriciansForums
Discuss S-type RCBOs in the UK Electrical Forum area at ElectriciansForums.net
reading
Does anyone make S-type RCBOs?
For discrimination you should use an S-type RCD to protect a sub-main feeding a CU with a normal 30mA RCD or RCBOs. This can be handled with a 100mA 100mSec S-type RCD. It would be convenient if this were combined with a type B or C 63 amp MCB.
This is in a domestic context with a main DB feeding a number of CUs.
Thanks for all your comments. Looks like a combination of tactics may be required as IssyS says: add mechanical protection where feasible, re-route the submains where feasible, or otherwise change the cables for SWA. Whatever tactic is used, the S-type RCDs don't add any useful additional protection and therefore the question I asked of whether S-type RCBOs are available is irrelevant.
Try answering my question!
If the distribution circuit is existing why are you looking to add RCD protection?
It's equally likely that each sub main is feeding a complete flat or dwelling so in that situation having a remote 30ma RCD feeding complete CUs would at best be hugely inconvenient in the event of tripping and at worst dangerous.
Reply to S-type RCBOs in the UK Electrical Forum area at ElectriciansForums.net
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...