Does anyone make S-type RCBOs?

For discrimination you should use an S-type RCD to protect a sub-main feeding a CU with a normal 30mA RCD or RCBOs. This can be handled with a 100mA 100mSec S-type RCD. It would be convenient if this were combined with a type B or C 63 amp MCB.

This is in a domestic context with a main DB feeding a number of CUs.
 
RCD required on submain consisting of 16mm2 T&E (not SWA) which is <50mm from surface of stud wall. Really you should use 30mA but then you don't get discrimination.

There's no "should really use" about it. If you are complying with the regs it has to be 30mA.

I'd be redesigning the distribution circuit installation myself.
 
RCD required on submain consisting of 16mm2 T&E (not SWA) which is <50mm from surface of stud wall. Really you should use 30mA but then you don't get discrimination.

Only 30mA non time delayed RCD protection is allowed for this application.

Presumably this domestic installation is split across multiple CUs? If so the having a single RCD protecting each CU is not really a problem as far as the regs are concerned.
For example, if you have an installation spread across two CUs each with an RCD main switch is it any different to having the whole lot on one split CU with 2x RCD?
 
Thanks for the comments. The submains already existed probably since pre-17th edition days protected by 63 amp MCBs. A risk analysis might suggest that the S-type RCDs would be better than none at all. It may be possible to change some of the more accessible cables for SWA which would solve the problem for some of them

But anyway thanks for the confirmation that S-type RCBOs are probably unavailable.
 
Thanks for the comments. The submains already existed probably since pre-17th edition days protected by 63 amp MCBs. A risk analysis might suggest that the S-type RCDs would be better than none at all. It may be possible to change some of the more accessible cables for SWA which would solve the problem for some of them

But anyway thanks for the confirmation that S-type RCBOs are probably unavailable.

As said, this will not comply with the requirements of BS7671 for alterations to existing circuits. You can either provide 30mA protection for the distribution circuits, change the installation of the distribution circuits so they do not require additional protection, or leave it as it is.
 
A risk analysis might suggest that the S-type RCDs would be better than none at all. .

Would it? If you take the purely mathematical view of the situation then it does appear that way. But what if you actually think about the purpose of the RCD?
30mA RCDs are designed to operate before death occurs in a person making contact with a live conductor, any delay in the operation and they will not disconnect before death has occurred.
Any RCD which operates after the death of the person might as well not be there at all from the point of view of that person.
 
Last edited by a moderator:
The 30mA RCD requirement is to (hopefully) prevent a fatal shock. A time delayed 100mA RCD doesn't do that, so you're wasting your time and money.

Add mechanical protection, re-route the submain, or change it for a cable type which will comply.

Protecting a sub-main with a 63A MCB is unlikely to offer discrimination for a downstream MCB anyway.

That's why switch-fuses take fuses, not circuit breakers.

I type too slowly!
 
Thanks for all your comments. Looks like a combination of tactics may be required as IssyS says: add mechanical protection where feasible, re-route the submains where feasible, or otherwise change the cables for SWA. Whatever tactic is used, the S-type RCDs don't add any useful additional protection and therefore the question I asked of whether S-type RCBOs are available is irrelevant.
 

Reply to S-type RCBOs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
658
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
855

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top