Hi Guys,
Would you all agree with me that this is the correct way for 3ph Safe isolation as I advised my apprentice of this and he has been knocked back by C&G as insufficient.
Prove Tester on known source or proving unit
Prove installation is Live
Switch off installation
Prove Tester on known source or proving unit
L1-L2
L1-L3
L2-L3
L1-N
L2-N
L3-N
L1- EARTH
L2-EARTH
L3- EARTH
N-EARTH
Prove Tester on known source or proving unit
Lock off
Retain key
Hang signs