Safe working practices. Q and A. | on ElectriciansForums
Discuss Safe working practices. Q and A. in the Electrical Course Trainees Only area at ElectriciansForums.net
SirKit Breaker
Ladies and Gents, trainees only to answer please.
Here are some questions that crop up in City and Guilds exams, and they are all about the basics, so if you don't know the answers, then you need to find them out. The last 2 are EAL NVQ3 knowledge questions.
  1. Which two pieces of equipment must you use to prove dead?
  2. Which non statutory document must the test leads comply with for the equipment in question 1.
  3. What are the 3 specific requirements for the test probe tips as laid down in the non statutory document in question 2
  4. On the load side of a single phase distribution board isolator, between which terminals would you test for dead.
  5. What would you do with the equipment in question 1, before using it, other than proving it works properly? (This also applies to any other test instrument)
  6. Above what voltage do the test leads need to comply with the non statutory document in question 2 and why?
  7. How many LIVE conductors are there in a single phase installation?
  8. Complete the following sentence. Lock off, Tag off, Post a notice, and ****** *** ***.
  9. If you discover someone who has suffered electric shock, lost consciousness then recovered, what must you do?
  10. If you discover someone having an electric shock, and you can't isolate them from the supply how would you safely remove them from the danger?
These will keep you busy for a day or 3, answers later in the week when you have had a chance to find out, but have a go at them. Enjoy......
The non stat doc in question 2 is free to download once you have found out what it is, and i suggest you do and print it off for future reference.
Cheers..............Howard
[ElectriciansForums.net] Safe working practices. Q and A.
Thanks Howard :wink:
Here are some questions that crop up in City and Guilds exams, and they are all about the basics, so if you don't know the answers, then you need to find them out. The last 2 are EAL NVQ3 knowledge questions. Answers in Red.
  1. Which two pieces of equipment must you use to prove dead?Approved Voltage Indicator and a Proving unit.
  2. Which non statutory document must the test leads comply with for the equipment in question 1. Health and Safety Executive Guidance sheet 38, aka GS38
  3. What are the 3 specific requirements for the test probe tips as laid down in the non statutory document in question 2. No longer than 4mm exposed tips, preferably 2mm and spring loaded.
  4. On the load side of a single phase distribution board isolator, between which terminals would you test for dead.Live to Neutral, Live to Earth, Neutral to Earth.
  5. What would you do with the equipment in question 1, before using it, other than proving it works properly? (This also applies to any other test instrument) Carry out a visual inspection of it
  6. Above what voltage do the test leads need to comply with the non statutory document in question 2 and why?50v, because lower than 50v is safe touch voltage.
  7. How many LIVE conductors are there in a single phase installation? 2, Line and Neutral are live conductors.
  8. Complete the following sentence. Lock off, Tag off, Post a notice, and Retain the key
  9. If you discover someone who has suffered electric shock, lost consciousness then recovered, what must you do? Send them to hospital.they may have internal injures that may not show for sometime.
  10. If you discover someone having an electric shock, and you can't isolate them from the supply how would you safely remove them from the danger? Use a non conductive piece of equipment with enough force to remove them from danger, but only if your own safety allows this. you should never place yourself in danger.
Answers for you in red. Anyone get them all right?
Reply to Safe working practices. Q and A. in the Electrical Course Trainees Only area at ElectriciansForums.net