Afternoon all,
I need some clarification regarding the use of a safety contractor and whether we can classify the safety contractor as a point of isolation. We have a control panel that requires inserting a castell key into the HMI unit to activate it. When we remove the castell key from the trap position, it disconnects the safety relay. Can this be used as the isolation point?
Thanks.
 
I would say yes and no.

it is most likely suitable for use as an point of isolation for mechanical maintenance.
however depending on how it is wired and what the safety systems in place on the machine are, it may not be.

this is one of the situations where people will have different opinions and the only correct one is a well thought out and documented Standard Operating Procedure.
followed up with detailed maintenance requirements if it is not going to be a simple "lock off main isolator before doing maintenance"

there is so much info needed to make a proper assessment of this that nobody can tell you remotely.
have you consulted the machine manufacturer?
 
Afternoon all,
I need some clarification regarding the use of a safety contractor and whether we can classify the safety contractor as a point of isolation. We have a control panel that requires inserting a castell key into the HMI unit to activate it. When we remove the castell key from the trap position, it disconnects the safety relay. Can this be used as the isolation point?
Thanks.
Contactors can be used for isolation, but not for safe isolation.
 
Table 537.4 indicates that contactors to BS EN 60947-4-1 are suitable for isolation as long as they are marked with symbol for isolation. With the caveat in 537.2.4 that devices for isolation shall be selected and or installed so as to prevent unwanted or unintentional closure. It then suggests means of achieving this eg padlocking.

I can find no differentiation in BS7671 between isolation and safe isolation. It is the same thing. At least according to the definition of isolation on page 37 "function intended to make dead for reasons of safety..."
 
Last edited by a moderator:
Table 537.4 indicates that contactors to BS EN 60947-4-1 are suitable for isolation as long as they are marked with symbol for isolation. With the caveat in 537.2.4 that devices for isolation shall be selected and or installed so as to prevent unwanted or unintentional closure. It then suggests means of achieving this eg padlocking.

I can find no differentiation in BS7671 between isolation and safe isolation. It is the same thing. At least according to the definition of isolation on page 37 "function intended to make dead for reasons of safety..."
The only safe way of isolating the power is to open a switch designed for that purpose and ensure the switch cannot be closed accidentally.

Contactors will have a higher rate of failing to open than a dedicated switch.

I suppose one that locks in the open position may comply but I’ve never seen one.

It will also have 2 supplies to contend with.
 
Last edited:
Table 537.4 indicates that contactors to BS EN 60947-4-1 are suitable for isolation as long as they are marked with symbol for isolation. With the caveat in 537.2.4 that devices for isolation shall be selected and or installed so as to prevent unwanted or unintentional closure. It then suggests means of achieving this eg padlocking.

I can find no differentiation in BS7671 between isolation and safe isolation. It is the same thing. At least according to the definition of isolation on page 37 "function intended to make dead for reasons of safety..."
isolation for reasons of safety could be a contactor that cuts the supply to a machine when a stop button is pressed it couldn’t be said to be safely isolated.

Safe isolation is more for maintenance and has its own procedure.


Existing safety standards give recommendations on how to apply contactors in functional safety applications. Regular operation of the equipment (opening and closing of the contactor) combined with a diagnostic control system (using the contactor’s mirror contacts) and a fault reaction function (system lock out, alarm, maintenance etc) enable the early identification of dangerous faults, increasing the safety reliability of the equipment. EV charger design standards already consider functional safety requirements in the basic design and consequently the design feature - electrical disconnection in the event of an open-circuit neutral fault built into the EV chargepoint, can be verified by reference to the existing standard 61851-1.

Contactors are designed to operate regularly (open & close) providing a simple and reliable method of remotely switching electrical loads on a regular basis. When using them in safety related applications, we should take note of the advice given in the contactor product standard 60947-4 and existing safety standards.
 
Last edited:

Reply to Safety Contactor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hello, We have been asked to install A Modicon Controller to provide PC control over an existing installation that has contractors/key switches...
Replies
0
Views
296
This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
3K
What performance level are you aiming for? It’s whole body access, so Pld or Ple? This is pretty much the first port of call before deciding on...
Replies
2
Views
1K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
Where in the supply are you going to isolate the panels ? What is the make model of your inverter ?
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks