I'm thinking, and while I could be wrong, is the adiabatic method a possible latent safety hazard? As well as undersized CPCs on circuits 32 amps and under?
Normally DNO sources are strong with relatively high PFC, and we have a known Ze value. However, should someone bring a portable generation unit on site after an outage, or a large yet short circuit limited inverter (Tesla Power Ball), Ze values can be such that MCB opening time increases. Such an increase can overheat the CPC, up to the point of melting it.
From a touch voltage perspective I humbly do not see a major concern however, in that 20 x 10 = 200 amps, 1.15 ohms or 46kw- a 46kw load on a 25kw generator would result in a significant drop in the output voltage whereby 230 volts dropping to 110 volts giving 55 volts to remote earth such that a longer disconnection time will not result in organic bodily injury.
However, the risk of fire and shock from an overheating CPC is relevant.
What do others make of this point of view?
Normally DNO sources are strong with relatively high PFC, and we have a known Ze value. However, should someone bring a portable generation unit on site after an outage, or a large yet short circuit limited inverter (Tesla Power Ball), Ze values can be such that MCB opening time increases. Such an increase can overheat the CPC, up to the point of melting it.
From a touch voltage perspective I humbly do not see a major concern however, in that 20 x 10 = 200 amps, 1.15 ohms or 46kw- a 46kw load on a 25kw generator would result in a significant drop in the output voltage whereby 230 volts dropping to 110 volts giving 55 volts to remote earth such that a longer disconnection time will not result in organic bodily injury.
However, the risk of fire and shock from an overheating CPC is relevant.
What do others make of this point of view?