Hi,
We’re having a new kitchen fitted, with a separate hob and double oven. The Hob is 6.4kW and the oven is 4.2kW totalling 10.6kW.
Would the below set up be ok for this?
Also, is the 4mm T+E ok as it’s protected by a 50A MCB? I was under the impression that any change down in cable size should be protected?
Any advice would be appreciated
Thanks
We’re having a new kitchen fitted, with a separate hob and double oven. The Hob is 6.4kW and the oven is 4.2kW totalling 10.6kW.
Would the below set up be ok for this?
- Consumer Unit with 50A MCB,
- 10mm T+E to 45A Cooker Switch (approx 13 metres),
- 10mm T+E to Dual Appliance Outlet (Scolmore 45A EASYFIT DUAL APPLIANCE OUTLET PLATE - https://www.superlecdirect.com/p-prw217-scolmore-45a-easyfit-dual-appliance-outlet-plate/),
- 4mm T+E to cooker and hob.
Also, is the 4mm T+E ok as it’s protected by a 50A MCB? I was under the impression that any change down in cable size should be protected?
Any advice would be appreciated
Thanks