I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system before it is sent to an event where people like me with 7909 then plug in and do some basic testing.
I've completed 7671 and other domestic install courses with a view to becoming fully qualified in time. At the moment I just work at the 7909 level with a pre done design provided by someone else.
Due to the distances we often run in events RCBO's are standard on every circuit. One thing I need clearing up is the requirements to satisfy both fault and over current protection for an RCBO. Max ELI on an RCD is given in table 41.5, so 1667 for a 30ma (obviously no one wants to see anything near that figure).....so no problem so far.
So if we have 100m run on 16a 2.5mm Ho7-RNF we need to be sure we're going to make 0.4/5s ADS. Am I right in the following thinking:
R1+R2/KM for 2.5mm HO7 is 7.41ohm. So for the 100m run it's going to be 0.74 ohms. We then refer to table 41.3 which give max ELI of 1.37ohms for a type c 16a MCB. Zs is likely in excess of 1.37 as we'll be TN-S and many hundreds of M to get our final 16a circuit (hence RCBO's on every circuit). As we're just using the protection for overcurrent and short circuit the same values are applicable to R1 + RN. Assuming that we're under the 1667ohms for earth loop we are then still making the disconnect times for fire and short circuit, PSCC? The RCBO is type c curve and so we'll be seeing in excess of 160a PSCC based on the values give in table 41.3?
Obviously this excludes any voltage drop considerations on the circuit but I want to check my understanding and thought process of reffering to the regs.
Thanks for the help
I've completed 7671 and other domestic install courses with a view to becoming fully qualified in time. At the moment I just work at the 7909 level with a pre done design provided by someone else.
Due to the distances we often run in events RCBO's are standard on every circuit. One thing I need clearing up is the requirements to satisfy both fault and over current protection for an RCBO. Max ELI on an RCD is given in table 41.5, so 1667 for a 30ma (obviously no one wants to see anything near that figure).....so no problem so far.
So if we have 100m run on 16a 2.5mm Ho7-RNF we need to be sure we're going to make 0.4/5s ADS. Am I right in the following thinking:
R1+R2/KM for 2.5mm HO7 is 7.41ohm. So for the 100m run it's going to be 0.74 ohms. We then refer to table 41.3 which give max ELI of 1.37ohms for a type c 16a MCB. Zs is likely in excess of 1.37 as we'll be TN-S and many hundreds of M to get our final 16a circuit (hence RCBO's on every circuit). As we're just using the protection for overcurrent and short circuit the same values are applicable to R1 + RN. Assuming that we're under the 1667ohms for earth loop we are then still making the disconnect times for fire and short circuit, PSCC? The RCBO is type c curve and so we'll be seeing in excess of 160a PSCC based on the values give in table 41.3?
Obviously this excludes any voltage drop considerations on the circuit but I want to check my understanding and thought process of reffering to the regs.
Thanks for the help