brightspark2010

Hi all just posting to see if anyone knew what is correct asked local wholesaler for a 3 phase 63amp schneider rcd they sent a 4 pole vigi and a 3 pole mcb. however at the site all other 3 phase ciruits supllied by 30ma vigis and mcbs are 4 pole switching the neutral would it be incorrect to not switch the neutral or do i require a 4 pole mcb the installation is tt?
 
If you have a TP & N circuit then you need a 4 pole breaker and 4 pole vigi unit. The 4 pole Vigi unit has tails of the correct length to connect directly to the 4 pole MCB complete with protective cover. Never have i seen a set-up, as you have described.... Be it on a TN-S, TNC-S, or TT system.

So how are you extending the neutral tail out of the Vigi unit to reach the DB's neutral bar(s)???
 
Not done it yet now waiting for the 4 pole mcb Iwis a bit unsure as to why they had sent the 3pole mcb to go with the 4 pole vigi i had thought it would come as 1 3 phase rcd unit then looking at the others in place it was obvious the neutral was switched for a reason just needed to know what that was. However schneider do say it is possible to join the neutral tail which is not copper bar as on old vigis to the bar if necessary.
 
I've been working with Merlin Gerin multi 9 stuff, for neigh on 30 years, i've never seen a Vigi unit with copper bars, they have always been tails, to connect to an appropriate MCB...
 

Reply to Schneider vigi and 3phase mcb in the Electrical Tools and Products area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
658
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top