Power down the panel, and measure continuity across the push button when it's pressed.

Hi mate, not sure what you know about these Pilz units but usually you have a dual safety circuit. And a reset circuit. There is usually 5 lights. 2 lights for each chanel on your safety circuit, both these lights should be on, if so, both channels will be made. You can then push reset which should send a low voltage back to the Pilz and providing all your required chanels are closed circuit (healthy) then the pilz contactor should pull in and your 2 output lights will come on aswell as your 2 chanel lights. When you press your reset button usually it also flags a light up o the pilz to let you know its fecievi g it.


check you havent got your chanels crossed. S11 to s12 and s21 to s22

Cheers for the explanation ..the fear was you were out on site trying to repair a machines critical safety system by asking a forum ...you can understand my hesitation to go any deeper without making it clear where you may have stood.... if this is just a test rig for personal training and not out in the field then a different matter altogether and would have helped a little to know in your opening post.
http://www.is-com.ru/files/PNOZ_X2_8P_en.pdf
Right then the wiring plan is here ^^^, you can easily check if you have a faulty start button contact block or broken wire by momenterally putting a link between terminals S12 and S34, if the relay resets then the problem is in your reset loop.


If it doesn't reset then your issues may be elsewhere and again you can prove it quite simply by removing wires and fitting links on the loop inputs to prove you have no open circuits on the loop you disconnected or simply use a meter to check your loops are closed.

Cannot tell you anymore without knowing which of the systems on page 3 of the link you have.

Looks ok, quickest solution is to power the panel down, then just go point to point with a continuity meter to prove everything is as it is on the drawing.



I did all the first page of the thread :) except to simply connect s12 and s34 because I noticed darkwood updated in the very last post with more instructions on that side.

UPDATE: There is continuity S11, S52 --> interlock and then S34 --> INT3
S12 --> S34 is fine once I push the reset button (of course)
then S21 --> interlock and S22 --> INT3

So with the panel power down it looks like there is NO continuity in the interlocks. BUT of course they are closed when I power up the machine because I can see the green light on each of the three!

Interlock brand is MECHAN, just for info.



So and please tell me if I am wrong, the issue is not in the safety loop.
 
Last edited:
There isn't a contactor on the feedback circuit stuck in?

Nothings been changed with the Pilz unit? Without looking up that particular model, some have a dial on the front to change if it is reset from a rising edge pulse or a falling edge etc...

Rob the model is PNOZ X2.8P

if there are not other considerations, I will carry on with the trials that darkwood gave to me

Please also find a further update with the feedback circuit (I believe it is this one...Am I wrong?)

SR_scheme_BIS.png
 
Last edited:
http://www.is-com.ru/files/PNOZ_X2_8P_en.pdf

We may be getting confused here .. which method do you think you have on page 3 of this link ...I'm under the assumption from the diagram you posted that you have a dual safety gate set up ie the 4 th down in the INPUT dual channel column... ?

This is the same connection set up with E - stops like 2nd option down same column.... connecting S11 to S52 gives monitoring of shorts between the separate loops...

PS I would also look into disconnecting all outgoing relays to ensure a fault on the 24vdc(asumming this is the control voltage) isn't dragging down the supply when you try reset you safety relay
 
Last edited by a moderator:
http://www.is-com.ru/files/PNOZ_X2_8P_en.pdf

We may be getting confused here .. which method do you think you have on page 3 of this link ...I'm under the assumption from the diagram you posted that you have a dual safety gate set up ie the 4 th down in the INPUT dual channel column... ?

This is the same connection set up with E - stops like 2nd option down same column.... connecting S11 to S52 gives monitoring of shorts between the separate loops...

With my humble level of knowledge of the subject, it looks like the same to me.....
 
With my humble level of knowledge of the subject, it looks like the same to me.....

They are the same just meant you using a monitored short circuit dual input set-up which is the same connections for E-Stops and Gates ...just to confirm we are all singing on the same hymn sheet here... are you using a 24v dc control for all your circuits running through the relays ...if so read my edit to last post.
 
They are the same just meant you using a monitored short circuit dual input set-up which is the same connections for E-Stops and Gates ...just to confirm we are all singing on the same hymn sheet here... are you using a 24v dc control for all your circuits running through the relays ...if so read my edit to last post.

yes 24vdc

I do not have here a jumper...there is no other way right?

I will need to buy one then...
 
yes 24vdc

I do not have here a jumper...there is no other way right?

I will need to buy one then...

All I meant by that was get a piece of wire and momentarally link said 2 terminals ...same as a link as though you were doing the job of the reset button with the short link of wire...

Site jargon --- Link - permanent connection eg 'link out terminals X an Y'
Jumper or jumper lead -a loose piece of wire for a temp' connection, I used the jumper because you don't wont to make a permanent link for the reset just mimic the action of the reset button.

When you get the hang of it you'll realise my little simple test routine takes about 2 mins and firstly confirms the relay is functional if it still has issues with loops linked out then disconnect all relay outputs to ensure no control short circuit is crashing the voltage and stopping the safety relay operating.

The hardest part usually is establishing which safety set-up has been implemented as safety relays can often be rigged up numerous ways to provide different cover and operation.

PS missed out in post 15 because you supplied the info after I posted is the link from s11 - s52 will also be required but the edit option in the forum has been reset and doesn't give you time to change things.
 
Last edited by a moderator:
All I meant by that was get a piece of wire and momentarally link said 2 terminals ...same as a link as though you were doing the job of the reset button with the short link of wire...

Site jargon --- Link - permanent connection eg 'link out terminals X an Y'
Jumper or jumper lead -a loose piece of wire for a temp' connection, I used the jumper because you don't wont to make a permanent link for the reset just mimic the action of the reset button.

When you get the hang of it you'll realise my little simple test routine takes about 2 mins and firstly confirms the relay is functional if it still has issues with loops linked out then disconnect all relay outputs to ensure no control short circuit is crashing the voltage and stopping the safety relay operating.

The hardest part usually is establishing which safety set-up has been implemented as safety relays can often be rigged up numerous ways to provide different cover and operation.

So I prepare a wire with two terminals and I connect with it the terminals S11 and S12, and then another one for S21 and S22.
But there will be no space to put a second terminal in S12 to connect with S34 :(

I did not understand the difference between permanent and temporary...If I do all these connections I am cutting out all the interlocks, emergency stop buttons, Safety contactors 1 and 2, Main contactor MC and also the relay R1.....is it not dangerous if I run the machine in this configuration?
 
So I prepare a wire with two terminals and I connect with it the terminals S11 and S12, and then another one for S21 and S22.
But there will be no space to put a second terminal in S12 to connect with S34 :(

I did not understand the difference between permanent and temporary...If I do all these connections I am cutting out all the interlocks, emergency stop buttons, Safety contactors 1 and 2, Main contactor MC and also the relay R1.....is it not dangerous if I run the machine in this configuration?


Yes just link out the terminals S11 to S12, S21 to S22 as well as another link from S11 to S52 then use a loose bit of cable to momenterally link S12 to S34.

If this then operates the safety relay it will only energise the control circuit ready for someone to push the start button or however its run...if you do not want to give them the chance to press anything just drop out your relay outputs so it will not energise the controls.

Once the unit is proven then you can remove the loop links straight away dropping the relay back out if its outputs are still connected, we are only talking a 10second window here that controls get powered so thats your call dependent on who's about, your line of sight and the risk level of the machine.
 
Yes just link out the terminals S11 to S12, S21 to S22 as well as another link from S11 to S52 then use a loose bit of cable to momenterally link S12 to S34.

If this then operates the safety relay it will only energise the control circuit ready for someone to push the start button or however its run...if you do not want to give them the chance to press anything just drop out your relay outputs so it will not energise the controls.

Once the unit is proven then you can remove the loop links straight away dropping the relay back out if its outputs are still connected, we are only talking a 10second window here that controls get powered so thats your call dependent on who's about, your line of sight and the risk level of the machine.

There is no space in S12 and S11 to put two cables...how may I do? May I connect in another place where the "original" S12 and S11 are connected like SC1 and Emergency button?

Also, I did not understand the windows of 10sec and this:

we are only talking a 10second window here that controls get powered so thats your call dependent on who's about, your line of sight and the risk level of the machine.
 
There is no space in S12 and S11 to put two cables...how may I do? May I connect in another place where the "original" S12 and S11 are connected like SC1 and Emergency button?

Compromise 'use a connector, smaller cables or dont ferrule them ' its just a temp' thing to check if it resets

Also, I did not understand the windows of 10sec and this:

Once you test the function of the safety relay by mimic of a reset button your relay may energise the outputs, this should not set the machine running it will only energise the control options to operate the machine, if you decide to leave the outputs connected that it, as soon as you have proven the relay you can immediatly open circuit one of the links you fitted and de-energise the enabled controls... you can do thin quickly hence I said the controls will only be energised approx 10seconds so up to you if you consider this a risk... if so drop out the relay outputs and the controls will not energise... try not to over complicate it, its easy to panic when your not sure and simple tasks then become confusing.. sit back understand how the relay operates and apply our help to what you have learned.
 
Yes I will tomorrow.

What about if I also try to disconnect all the wires from: 13 23 33 14 24 34 and keep only 41 and 42 (and of course the power for the SR A1 and A2) for the lamp and also try this...

If I power on and the button works, it might be something wrong outside the couple SR + its safety loop.

Am I wrong? (Maybe someone else adviced this but I didnt get?)



Really thanks anyway to everyone!!!
 
Last edited:
Yes I will tomorrow.

What about if I also try to disconnect all the wires from: 13 23 33 14 24 34 and keep only 41 and 42 (and of course the power for the SR A1 and A2) for the lamp and also try this...

If I power on and the button works, it might be something wrong outside the couple SR + its safety loop.

Am I wrong? (Maybe someone else adviced this but I didnt get?)



Really thanks anyway to everyone!!!


Lets reflect here as your getting all confused ...


Power terminals A1 + A2 power supply - leave as is.

Relay terminals ......N/C 41 - 42 usually trip indicator -leave as is.
N/O 13 - 14 / 23 - 24 / 33 - 34 (disconnect 14,24,34 if you don't want to energise the machine controls while testing unit.

Monitoring circuits
The unit has to see a closed loop between terminals S11 and S12 (this is for your loop 'A' of the E stop system)
The unit has to see a closed loop between terminals S21 and S22 (this is for your loop 'B' of the E stop system)

The unit has to see a closed loop between terminals S11 and S52 (this configures the unit to monitor any shorts between the above loops)

When the unit see's all these above conditions met on the monitoring loops then a momentary connection from S11 to S34 should operate the unit and the relays will change over to allow power to the control system of the machine.

When you understand what the unit is doing then you can decide (as I have shown you) how to confirm the safety unit is working by disconnecting loops and linking the appropriate terminals.
Once you get to grips with this one then there are many more combinations of safety relays and set-ups to work out ...this one been a very simple one to learn on.
 

Reply to Schneider ZBE 101 is not working in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
683
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
969

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top