Hi guy as from title I am after a 2nd opinion on coding faults I have found during a EICR of a hotel and there are a few (wouldn't believe it's a 5 star!)
The most common is light switch inside bathrooms, a touch plate I.e hover your hand over it and it will dim etc. Now these are installed within zones 2 & 3 within the hotel covering 89 rooms, they are also metal plates and not earthed. I have these as code 2 (potential danger)
The next one is taps not earthed in bathrooms intermittently throughout the 89 rooms but half of them have all circuits covered by RCBO whilst the other half not all the circuits if any have RCBO/RCD protection. Again I have C2 them potential danger.
Next one I have intermittently installed non Ip rated downlighters above showers, say 50 in total. I have C3 these (improvement recommended)
I have also noted that we have issues with the downlighters as they are not fire rated, throughout, now the ones that are fire rated have LED lamps installed which I now believe is a big no no as LED disperses the heat out the top so a lighting cage must be used?
Does anyone have any views on this?
Cheers in advance
The most common is light switch inside bathrooms, a touch plate I.e hover your hand over it and it will dim etc. Now these are installed within zones 2 & 3 within the hotel covering 89 rooms, they are also metal plates and not earthed. I have these as code 2 (potential danger)
The next one is taps not earthed in bathrooms intermittently throughout the 89 rooms but half of them have all circuits covered by RCBO whilst the other half not all the circuits if any have RCBO/RCD protection. Again I have C2 them potential danger.
Next one I have intermittently installed non Ip rated downlighters above showers, say 50 in total. I have C3 these (improvement recommended)
I have also noted that we have issues with the downlighters as they are not fire rated, throughout, now the ones that are fire rated have LED lamps installed which I now believe is a big no no as LED disperses the heat out the top so a lighting cage must be used?
Does anyone have any views on this?