All of the work described below will be completed by a qualified electrician, I am just curious and using the info for planning!!
I am planning a garage conversion. While I was bringing across services for water/gas etc I laid a 16mm2 3 core SWA between the main dwelling and the garage (all at the correct depths and signed of by building control) which will feed a secondary consumer unit.
In terms of connecting the SWA, I am trying to determine the best way to achieve max load to the secondary consumer unit in the garage conversion because it will draw significant power including:
The SWA is 15 meters long and according to TLC Direct voltage drop calculator I have a max load of 87 Amps so I was thinking of protecting using something around 80 Amps:
Very very basic diagram looks like this:
As far as I see it I have the following choices:
What would be the cleanest and best solution?
I am planning a garage conversion. While I was bringing across services for water/gas etc I laid a 16mm2 3 core SWA between the main dwelling and the garage (all at the correct depths and signed of by building control) which will feed a secondary consumer unit.
In terms of connecting the SWA, I am trying to determine the best way to achieve max load to the secondary consumer unit in the garage conversion because it will draw significant power including:
- Washing machine
- Tumble dryer
- EV Charger
The SWA is 15 meters long and according to TLC Direct voltage drop calculator I have a max load of 87 Amps so I was thinking of protecting using something around 80 Amps:
Required Cable Size | 16mm |
---|---|
Voltage Drop | 3.26 Volts |
Percentage Drop | 1.4% |
Current Load | 87.0 Amps |
Max Cable Load Max Cable Load refers to the maximum allowable current for the cable used in the configuration given above and will vary considerably under different configurations. | 94.0 Amps |
Very very basic diagram looks like this:
As far as I see it I have the following choices:
- Following the supply isolator, Henley block to split into fused main switch (80 amp) and the other side into the consumer unit
- Problem: fused main switches do not seem to have cutouts for SWA glands so I would need another ugly box where my meter stuff is to terminate the SWA
- RCBO using a spare way in the consumer unit to feed SWA
- Problem: Hager RCBOs seem to go up to 40 Amp, I would have to mix and match RCBO brands to get 80 Amps
- Something else inside the consumer unit (MCCB or RCCB?)
What would be the cleanest and best solution?