Does secondary gas meter to be earthed .
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss secondary gas meter in the UK Electrical Forum area at ElectriciansForums.net
Gas pipework doesn't require earthing, may require BONDING thoughDoes secondary gas meter to be earthed .
Need more information. Is the secondary meter in separate sub accommodation with its own electricity supply with its own CU?Does secondary gas meter to be earthed .
The primary gas meter is earthed to the main distribution board , but the gas meter is outside, the pipe work is on the outside goes down the side of building. flat has its own cu . secondary gas meter is bonded to other pipe work inside the building but not earthed to the flats cu.Is there bonding to the gas pipe going to the first meter?
Is the second gas meter in the same building as the first?
How is the second gas meter connected to the first... e.g. route of pipe?
But! If the primary gas meter has a plastic gas main pipe entering the building then there is no extraneous metal on the gas supply, then no need to connect the earth cable to the metal outlet of the primary or secondary meter.
What about the accommodation that the sub meter services? Slf contained with its own electricity supply with CU?The primary gas meter is earthed to the main distribution board , but the gas meter is outside, the pipe work is on the outside goes down the side of building. flat has its own cu . secondary gas meter is bonded to other pipe work inside the building but not earthed to the flats cu.
If the plastic main enters the building that is so. If the meter is outside with plastic main with the outlet pipe entering that is not extraneous. Outlet gas pipes are supposed to be in plastic sleeving or wrapped, so no ground or wall masonry contact. If there is it is a cowboy job.This is incorrect, a plastic incoming main does not automatically mean that the installation pipework is not extraneous. If the installation pipework is metallic and in contact with the ground, possibly via burial in concrete or the building fabric, then it may well be extraneous.
If the plastic main enters the building that is so. If the meter is outside with plastic main with the outlet pipe entering that is not extraneous. Outlet gas pipes are supposed to be in plastic sleeving or wrapped, so no ground or wall masonry contact. If there is it is a cowboy job.
You are right about years ago. Even iron gas pipe has to be protected. There should be no contact of any gas pipe, not matter what material it is made of, with masonry. It is worthless bonding to a meter with plastic main pipe.Whether it is a cowboy job or not it would still require main bonding as a result of it.
Years ago this was not a requirement and you will still often come across buried iron gas pipes in an installation which are extraneous due to their being buried on the consumers side.
Making the statement that a plastic incomer automatically makes all installation pipes not extraneous is incorrect in my opinion and it would be very bad practice to make such assumptions without carrying out testing to prove otherwise.
You are right about years ago. Even iron gas pipe has to be protected. There should be no contact of any gas pipe, not matter what material it is made of, with masonry. It is worthless bonding to a meter with plastic main pipe.
Always assume all gas pipes were all fitted properly not assuming a cowboy job, or something installed in the 1950s, which is what you saying you do, to get some electrical bonding.'should be' is a wonderful phrase that doesn't always mean much in the real world. There are lots of 'should be's' in the world which just aren't.
I stand by my point, the pipework should be tested to establish whether or not it is extraneous rather than making assumptions based on what 'should be'