wannabesparky

can anyone tell me if it is possible to install a security flood light coming from an upstairs ring main as a socket is close to where the light needs fitting but the occupant doesn't want any cables or anything showing outside or the decor disturbing inside in any way.
is it possible to put a fused spur next to the socket and come off that and if so what fuse would be used?
it is a 250w flood light

only just started to take up my college work again.
sensible answers only thank you.
 
is that ok for a 500w flood light aswell

Someone not listening in here? Eh? Pardon? What?

Let's speak CLEARLY for the chap here........

Simple maths. Simple maths that you learn in the first few DAYS of any college course. You haven't studied for a while, OK, but come on, what have you been doing to forget even the basics? Are you honestly sure you should have that screwdriver anywhere near mains?

230VAC supply. 250 Watt fitting. Watts/Ohm's Law.... V x I = P voltage times current = Power, or in this case - you want to find current, so.... Power, divided by voltage = Current. 250/230 = 1.08A - 3A fuse.

230VAC Supply. 500W fitting. Same sum, off we go......

500/230 = 2.173913A, call it 2.18A = use a 5A fuse for longevity.

Not rocket science.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
security flood light
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
wannabesparky,
Last reply from
accordfire,
Replies
15
Views
11,875

Advert

Back
Top