Hi,
Our house is 150m away from the street. We installed a 600V step-up/down system to bring electricity to it in order to avoid excessive losses and very large cables. The 240V/600V 50KVA transformers are rated NEMA-3R enclosures, located one 10ft above ground and the second one 5ft above ground.
Last week we have got a nasty storm (heavy rain, strong winds and lightning everywhere). Of course, one bolt hit the installation and both transformers blew-up. They have been replaced and I decided to analyze the system. Below is the schematic as I could make it. I am wondering if there is a grounding issue.
Regarding the causes of the blow up, I think the combination of NEMA-3R, the heavy rain and the wind allowed water to enter the step-down transformer. Then the lightning strike created an arc that have been maintained by the utility company power feed. The main breaker did not trip fast enough. We heard the transformer humming like crazy for about one second. The aluminum windings have melted. I suspect the breaker tripped because of over current (>200A), not because of ground fault. This may be the reason it took so long to trip.
In the diagram the black lines are what exists today. The red lines is what I think is missing.
Any advice?
Thanks in advance.
Our house is 150m away from the street. We installed a 600V step-up/down system to bring electricity to it in order to avoid excessive losses and very large cables. The 240V/600V 50KVA transformers are rated NEMA-3R enclosures, located one 10ft above ground and the second one 5ft above ground.
Last week we have got a nasty storm (heavy rain, strong winds and lightning everywhere). Of course, one bolt hit the installation and both transformers blew-up. They have been replaced and I decided to analyze the system. Below is the schematic as I could make it. I am wondering if there is a grounding issue.
Regarding the causes of the blow up, I think the combination of NEMA-3R, the heavy rain and the wind allowed water to enter the step-down transformer. Then the lightning strike created an arc that have been maintained by the utility company power feed. The main breaker did not trip fast enough. We heard the transformer humming like crazy for about one second. The aluminum windings have melted. I suspect the breaker tripped because of over current (>200A), not because of ground fault. This may be the reason it took so long to trip.
In the diagram the black lines are what exists today. The red lines is what I think is missing.
Any advice?
Thanks in advance.