OK,
I asked the akward questions:
Earthing and RCD's
Euorocode 5
Earthing / Bonding
TL inverters - earthing / bonding (as per the decision tree) from both SMA and Fronius was unambiguous, - DO IT, don't risk the chance of slight shock to an aerial installer or the like (velux windows..) at a later date, it he fell off a ladder, H&SE will investigate and start asking lots of questions which will probably result in a retrofit requirement.
RCD's interesting here.... For Fonius and SMA, which have built in DC injection protection Type B's are NOT required.
Ideally configire the installation so that an RCD isn't required.
Where BS7671 requires an RCD, use Type A 100mA, where 30mA is required by BS7671, try in the first instance to reconfigure it so it isn't need, if all else fails, then the problem of nuisance tripping can in most instances be overcome if you use a Wylex RCD (said a bit under the breath - must be something to do with the spec - who said quality - of the Wylex kit).
Eurocode 5 and Slate roofs.
Slate:
Schuco dead against anchor bolts for slate, they don;t see how it is compliant despite a numberof their customers using hanger bolts exclusively, use iether of their 2 slate hooks, one screws through the bottom slate, longer one goues over the top of the slate, lead over and dress the top slate around. They promised photos and written instructions..
Eurocode 5:
In 35-38mm trusses, either properly installed reinforcement or noggins, both of which require access to the internal roof space, so won't work on loft conversions. They promised photo's and instructions ...
Hope that helps