I’m carrying out a PIR on a three storey house (sheltered accommodation) with one lighting circuit for the whole property.


For the purpose of safety and convenience it should have two lighting circuits and/or have emergency light.



Would this warrant a code 4 or just a mention in the report?
 
Segregation of circuits refers to segregating LV and ELV circuits.
I think you are refering to division of circuits. In wich case you should consider Regulation 314.1 especially (i) avoid hazards and minimize inconveience in the event of a fault and (ii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit.
Applying a code 4 suggests that you do not consider the situation to be a danger, whereas a code 2 would suggest that the situation is dangerous, but not immediately so, but needs rectification.
 
Last edited by a moderator:
Thanks spin!

DIVISION of circuits Doh! That's what I was refering too!

The english language is a wonderful tool for communication when you get it right! ha!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Wales

Thread Information

Title
Segregation of circuits
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
Dic Penderyn,
Last reply from
Dic Penderyn,
Replies
2
Views
4,940

Advert

Back
Top