I have a small Consumer Unit fed from a 6 amp type B mcb to a 6 amp type B,it only feeds 1 light in a bin store .
clearly we have no selectivity here ,would changing the feed mcb to a type C possibly 10 amp help achieve this?
its only on 1.5 swa so I can’t go too high ,my ZDB is 1.05 ohms
 
Last edited:
You need to look at pages 416 and 417 of regs book, and also see if the MCB manufacturer publishes a selectivity chart (assuming they are both same brand).
 
the time current curves don’t appear to say , also I guess they will only be selective for over currents , at a fault current of 228 amps there cant be any selectivity Eaton seem to suggest?
[ElectriciansForums.net] selectivity 60898 b6 to same
 
the time current curves don’t appear to say , also I guess they will only be selective for over currents , at a fault current of 228 amps there cant be any selectivity Eaton seem to suggest?

As a general rule of thumb for MCBs within the standard range of 6A - 63A they don't achieve selectivity on fault currents.

This is why MCBs are generally unsuitable for protecting distribution circuits.

BS88 fuses on the other hand have a selectivity ratio of 1.6 so if an upstream fuse is rated at least 1.6x the rating of the downstream device you will get selectivity.
 
As suggested above, you don't need the 2nd MCB here. A switch would do if some local means of isolation is needed.

However, is it a problem? True under fault conditions it is pretty much sure both will trip, but if that likely to present danger or unacceptable trouble for the owner?

If the supply was from another locked location I can see why it would matter, but if it is just two locations within one property, and nothing else is dependant on the upstream MCB remaining closed, then not worth worrying about.
 
I have changed the supply to a 16 amp mcb , my ZS at the bin store light is 1.29 ohms ,fault current of 186 amps.
my read of the time current curves is that the local 6 amp will trip possibly the 16 amp as well ,so I may not have achieved much at all!
[ElectriciansForums.net] selectivity 60898 b6 to same
 

Reply to selectivity 60898 b6 to same in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top